8.5 KW shower on 40amp mcb and 6mm??

Discussion in 'Electricians' Talk' started by Frank Spencer., Oct 11, 2009.

  1. Frank Spencer.

    Frank Spencer. New Member

    hi all, is it okay to run a 8.5kw shower on a 40amp wylex mcb ,cable size is 6 mm, clipped direct . it is currently on a 30 amp rewirable fuse(the old shower) but the new shower will be 8.5kw also on to a mcb. So should i put it on a 40amp or 32amp.thnks if any of you can reply ,Frankie
     
  2. 14th edition

    14th edition Well-Known Member

    40A is too high for 6mm, should be 32A. Also the length of the cable run has a big impact on whether 6mm is a big enough cable.....! Its generally ok but can struggle for long runs.

    14th
     
  3. Lokkars Daisy

    Lokkars Daisy New Member

    sorry to disagree 14th but the 40A mcb will be fine as likely as not will also be the cable
     
  4. Adam Amp

    Adam Amp New Member

  5. pcelectrics

    pcelectrics New Member

    An 8.5kW shower draws a current of 35.5A.

    So, you need an MCB higher than this value. Next size up is 40A. So okay there.

    You now need a cable with a higher rating than 40A. BS7671 table 4D2A under ref method C (clipped direct) shows the smallest cable with a rating over 40A is 6mm with a rating of 46A. Table 4D5A gives 6mm flat T&E clipped direct a rating of 47A. So okay there.

    So, all okay then!

    If at any point the cable needs to pass through the insulation layer in a loft, make sure there is an air space around the cable. I use 100mm waste pipe for this purpose, but if the cable is already in place you could build a plasterboard or chipboard box around the cable.
     
  6. Frank Spencer.

    Frank Spencer. New Member

    cheers for yout reply guys, so a 40amp will be okay on the 6mm so long as it is not a long run and not surrounded in insulation.
     
  7. JP.

    JP. Screwfix Select

    Clipped direct..the cables well in..cripes its showing 4mm @ 12 meters and over @ 8500 Watts..cable on the TLC site shows 40 Amps..

    No probs from what I can see..however I am not a sparky so what I say doesn't really count.
     
  8. JP.

    JP. Screwfix Select

    Do you use Steradent? or do you use a supermarket own brand denture steeper to steep ure gnashers Lucia?
     
  9. 14th edition

    14th edition Well-Known Member

    Have I missed something here?! I have page 282 table 4D5 [can't find a 5A]. The highest for 6mm t/e is 47 for clipped direct, in my experience extremely unlikely. Much more to be in a wall and or under loft insulation so 27-34 amps.And thats disregarding volt drop.
    Agree cable length is rarely a problem but I still think that to protect the cable 32A is better and they rarely trip until that is exceeded by some margin. I think that that is the problem with a 40A mcb it could be running at way over without tripping the mcb.
    IMHO

    14th
     
  10. Lokkars Daisy

    Lokkars Daisy New Member

    The current is limited to the shower rating, in this case around 37 amps.
     
  11. Removed 4

    Removed 4 New Member

    Do you use Steradent? or do you use a supermarket own
    brand denture steeper to steep ure gnashers Lucia?


    I just use wire wool every fortnight, without fail, JP.

    I do have Steradent in the bathroom cabinet, as a stand-by, just in case I'm invited out to dinner and I need that extra sparkle.......



    Lucia x
     
  12. 14th edition

    14th edition Well-Known Member

    Lokkars, aren't we supposed to be protecting the cable....?

    14th
     
  13. Lokkars Daisy

    Lokkars Daisy New Member

    In this case the mcb will provide short circuit protection to the cable, providing overload protection for the cable by using an mcb isn't required. The reason being that as the load is fixed then an overload is very unlikely to happen. This is all above board, it's a similar situation to the use of light guage flex in pendants, the flexes are often rated less than the 6A mcb
     
  14. Removed 4

    Removed 4 New Member

    Duncan, I can see you point here. You would rather fit a 32A mcb to carry 37A in the knowledge that the mcb would take a few weeks to trip. But we're not supposed to design a circuit where the load exceeds the rating of the mcb, are we?

    A 6mm cable will be protected by a 40A mcb, whatever the circumstances - regardless of this loft insulation nonsensense. This shower is a dedicated fixed load. It cannot be added to by other loads. There's only two considerations here: The design current and the short-circuit fault current.


    Lucia x
     
  15. Removed 4

    Removed 4 New Member

    Good evening, Lockheart. I seem to have duplicated your reply....


    x
     
  16. Lokkars Daisy

    Lokkars Daisy New Member

    Good evening Lucia, yes indeed but with that Italian flair of your'un
     
  17. Lokkars Daisy

    Lokkars Daisy New Member

  18. seneca2

    seneca2 New Member

    I cannot beleive how ridiculously long this post has become! 8.5Kw shower, 6mm t/e, 40 amp breaker, no problem at all!
     
  19. Removed 4

    Removed 4 New Member

    Steady on Sen! This is only page 2, dear.......



    x
     
  20. 999

    999 New Member