    Looking at Sundial C plan, is a 1.5mm T&E protected by a 6 A MCBO ok from consumer unit to Honeywell junction board? Will have a 3 amp fused switch as per boiler and controller documentation.
    I'm assuming because it is fused at 3 amp, no real need for 2.5mm cable and 16 amp RCBO
     
  2. I assume you mean an R.C.B.O yes it will be ok,but I always run 2.5.
     
  3. mrppp

    mrppp Active Member

    yes R.C.B.O :) And use a 16A R.C.B.O
     
  4. seneca

    seneca Screwfix Select

    Correct mrppp, no need for 2.5mm cable or 16 amp breaker for this!
     
  5. Joe95

    Joe95 Screwfix Select

    That'll work, I have a condensing combi three zone system with the Nest thermostat - That is all run off a 10a RCBO and 1.5mm cable and a 3a fuse at the FCU
    The 16a and 2.5mm is usually for when an immersion heater is fitted.
     
  6. mrppp

    mrppp Active Member

    So maybe run 2.5mm and 16A run to a 20amp double pole isolator switch that way i could fit emersion if required i guess at later date
     
    Joe95 likes this.
  7. You need a fused connection unit with a 3 amp fuse for your boiler and controls.
    You could run a radial from a 20amp RCBO with the fcu for boiler and 20 amp double pole switch for immersion heater, although I like to keep immersion on its own circuit.
     
    Last edited by a moderator: Sep 30, 2016
  8. mrppp

    mrppp Active Member

    Ok going to run 2 x 2.5mm T&E one for immersion and one for controls, both on isolation switches both on own RCBO. Got it all covered then:)
     

Share This Page