boiler flow issues

Discussion in 'Plumbers' Talk' started by warey4life, Oct 3, 2015.

  1. warey4life

    warey4life New Member

    Hello All,

    I am putting a new bathroom in. At the moment I am taking tiles off the wall so had to take the radiator off. I am fitting a new radiator when the tiling is finished.
    My problem is, I went to switch the heating on today and the boiler has a flow issue, the flow temp rockets up to 90c. I don't understand why this is because the radiator I took off had a bypass between the flow and return pipes that went to the radiator so surely I still should have flow around the system??

    Please help :)
     
  2. warey4life

    warey4life New Member

    I've put the rad back on, refilled and bled, still the same :(
     
  3. warey4life

    warey4life New Member

    Panic over, Sorted it now. The AAV on the boiler was blocked solid and the boiler must have been air locked.
     