Hello all Can anybody tell me where I can purchase 16mm2 concentric (or straight concentric cable) (not split contric)by the meter please? Many thanks WLX
Ask any electrical wholesaler (useful one that is, not a 'shed' like SF) for it . They'll get it for you. It's BS7870 cable, BTW.
Any wholesaler can deal directly with any cable supplier, and while they would usually be purchasing split concentric, they will be able to obtain straight concentric just as easily. You may find the counter staff are confused, but be persistent in your "straight concentric" request. I do have to ask though......what's it for! It's not covered by BS7671, and never has been.
It is an off grid farm (generator) distro to all sheds is PME TNCS CNE 1 new shed got a cutout but cant get the cable! Many thanks will try some persistance
You might struggle to get hold of the straight concentric, DNO use only, split con on the other hand is ace, terminate it like twin and skin
Although the neutral is connected to earth internally at the generator, all generator outputs I have seen have been LN&E, this to me is a TNS supply. Are you just distributing the L&N from the generator, if so sounds more like TT than TNCS, whats the earth rod situation?