  1. sparky Si-Fi

    sparky Si-Fi Screwfix Select

    My sincere apologies for the dumb arithmetic!

    Thats what you get for rushing cable calcs prior to going on site.

    Thanks for the kick in the balls Spin
     
  2. Dale76uk

    Dale76uk Guest

    Interestingly, the NICEIC helpdesk called me back and refered to the OSG page 41 (green) and the top line reads something like 'For PME systems the DNO may require the Earthing Conductor to be 16mm'

    Voila, so if the DNO are happy with a calculated EC then its okay.   ;)
     
  3. Lokkars Daisy

    Lokkars Daisy New Member

    Interestingly, the first known use of 'voila' was in 1739
     
  4. spinlondon

    spinlondon Screwfix Select

    Still needs to be a minimum of 10mm² to comply with BS7671.
     