Hob + Oven wiring

Discussion in 'Kitchen Fitters' Talk' started by clifford83, Sep 12, 2017.

  1. clifford83

    clifford83 New Member

    Hi

    I am picking up a hob tomorrow which is rated at:
    28.1a
    6500W
    7.22kw

    I have a 32a spur which has a socket and a hard wired socket. I have always had a freestanding cooker and had it hard wired which is fine. But since im going for integrated appliances i wanted to know if i could hard wire both HOB + OVEN to the one 32a hard wired socket?. Or would the load be too much?.

    I haven't got a oven yet, and the one im after actually doesn't list the power specifications!. Annoyingly.

    IF i do opt for a 13a plugged oven, can i simply plug it into the cooker plug socket or again, would the load be too much together with the hard wired hob?.

    Cooker connections are about 22ft from the fuse box. And on the fuse box for the cooker it states as follows:
    TYPE OF WIRING: A
    NUMBER OF POWER POINTS: 2
    CIRCUIT CONDUCTORS: LIVE 6MM / CPC 2.5MM
    OVERCURRENT PROTECTION BS(EN) 61003
    RATING: 32A
    CAPACITY: 6KA
    OPERATING CURRENT: 30MA
    MAXIMUM ZS PERMITTED BY BS7671: 1.44

    Advice please.
     