Hot water is 37°C max

Discussion in 'Getting Started FAQ' started by Ilia, Jun 19, 2017.

  1. Ilia

    Ilia New Member

    Hot water is 37°C max just 2 months after a new boiler installation
     
  2. terrymac

    terrymac Screwfix Select

    under warranty ,get installer back to sort problem .
     
    KIAB likes this.
  3. Ilia

    Ilia New Member

    Thank you for your reply! The installer claims boiler is functioning properly and suggests to supply and fit a new cylinder and new immersion heaters to resolve the problem. Is there any way to get an objective opinion on what is the actual issue ?
     
  4. At the very least we need to know make and model of boiler, type of hot water storage system, what the 'stat on that cylinder is set to, and whether the hot water was hotter before this boiler was fitted - is the boiler the only thing that was changed?

    And what type of boiler did you have?
     
    terrymac likes this.
  5. CraigMcK

    CraigMcK Screwfix Select

    Just to be clear do you have immersion heaters switched on in the current setup? or have you always relied on the boiler heating up the tank?
     
  6. Ilia

    Ilia New Member

    Thanks for your feedback! The old Flamingo CF boiler was over 15 years old, and started malfunctioning (was switching off). It was replaced by Vaillant ecoTEC plus OV 418 2 months ago. The cylinder is also over 15 years old, model : Telford Indirect. Cylinder settings remain unchanged since boiler was installed. The water was hot enough for about 2 months after the new boiler was installed. The temperature suddenly dropped to about 37C last week. Now boiler screen shows 27C. I believe the immersion heaters were always on as well as the boiler.
     
  7. KIAB

    KIAB Super Member

    Bad practice fitting a new boiler, & leaving a 15 year old cylinder in place,as for trouble, should have replaced the lot.
    Old cylinder is problely seriously scaled up & restricting flow & the heating of hot water.

    [​IMG]


    upload_2017-6-20_11-57-26.jpeg
     
    Last edited: Jun 20, 2017
  8. CraigMcK

    CraigMcK Screwfix Select

    Not familiar with Vaillant boilers, do they show the water temp on the display when running?

    Has it possibly been set to "summer" mode on the likes, while I agree scale could be an issue, it's not likely just to drop from hot to not overnight. Which part of the country are you in?
     
  9. KIAB

    KIAB Super Member

    Another one not familar with the Vaillant ecoTEC plus OV 418, (like my Valliant combi's) but it has a summer mode for heating & a quick nosey at manual you can set hot water temperature, see linky below.

    https://www.google.co.uk/url?sa=t&rct=j&q=&esrc=s&source=web&cd=7&ved=0ahUKEwiy842usMzUAhVHAsAKHZ4aBWMQFgh4MAY&url=https://www.vaillanthome.co.uk/download/ecotec-plus-open-vent-user-manual/&usg=AFQjCNEJmKbDQ5xyFJkF3SAR_NAzuEwCzw

    If scaled up cylinder, could crud in it cause an obstruction in HW heat exchanger & boiler safety feature is reducing HW temperature.:confused:

    Also there is a Frost setting on boiler which works with heating & hot water which is set at 30 degrees.
     
    Last edited: Jun 20, 2017
  10. Ilia

    Ilia New Member

    Many thanks to everyone for the additional feedback! Just spoke to the boiler manufacturer's technical support, and they have walked us through the boiler controls and concluded that the boiler switches on and then off again. They suggested the issue could be caused by malfunctioning of 'stats inside the cylinder, as in 'stats being unable to send correct signal to the boiler. This in turn could be caused by cylinder scaling or aging according to Vaillant's advice. If this sounds about right, what would be the ballpark figure to replace the cylinder and the cylinder related devices such as immersion heaters etc? The flat is in Hendon, London NW4.
     
  11. KIAB

    KIAB Super Member

    Yes :eek: :oops: [​IMG]

    What size/ capicity is the present cylinder.

    I thinks your installer totally screwed up, any decent installer would have recommended replacing the cylinder because of it's age, unless OP asked to keep orginal.
     
  12. Ilia

    Ilia New Member

    something like 450 x 900. The installer suggested replacing it with 400 x 1050 size.
     
  13. Pollowick

    Pollowick Screwfix Select

    A limescale build up will not stop the water being heated - it may allow an initial overheat. The hot water at say 80c passes through the coil, any deposits act as a buffer and slow transfer to the stored water which will gradually rise to the nominal 65 degree cut off. However, limescale on the cylinder will act as another buffer and it will take time for the thermostat to register 65, water may well be 70 or 75 initially but equilibrium will soon occur. There is no way that the stat on the outside could register a temperature higher than that of the stored water.

    Try adjusting the stat up and down a few times before returning to the normal temperature.


    Think about a water softener too.

    I have just opened up my cylinder for a look with the intention of replacing it as I am in a very hard water area. It has been in place for 25 years or so with a water softener running for the last 8 or 9 and when the previous cylinder was removed - it was similar to those pictures. When I looked inside - there was just a fine almost dust like coating and no layers - teh softener certainly works and over time the water has reabsorbed some of the scale hence there is none present.
     
    KIAB likes this.
  14. Pollowick

    Pollowick Screwfix Select

    Why?

    A 450x900 has a capacity of 117 litres and a 400x1050 is 114 l so there is a small loss. Would be more sensible to stay as is or move to a 450x1050 with an extra 20% at 140 l.
     
    KIAB likes this.
  15. KIAB

    KIAB Super Member

    Agree Mr P.

    A 450x1050 would be the better option.
     
  16. KIAB

    KIAB Super Member

    Best idea is rip the lot out, & replace with a combi or system boiler with unvented cylinder.:)
     
  17. Pollowick

    Pollowick Screwfix Select

    Unvented still have scale build up issues.

    Water softeners are a must in some places.
     
    KIAB likes this.
  18. Ilia

    Ilia New Member

    Appreciate the detailed explanation. Looks like the consensus is towards replacing the old cylinder and Co , and once replaced start using the softener to to avoid scale build up. Any idea how much labour+parts should cost for this type of job (in London)?
     
  19. Mike83

    Mike83 Screwfix Select

    This model is open vented so could be an airlock.
    Do the flow and return pipes at the cylinder both get quite hot?
    The cylinder could be perfectly fine.
    What is the boiler stat set at? I usually set it about 68 degrees to ensure cylinder can reach 65 via the cylinder stat.
    If using a normal cylinder stat ignore what the hot water stat on the boiler says as this won't be functioning.
     