Im looking into a scenario where a distribution circuit to a shed is to be taken from a henley block near the meter. Its a TN-S system. The dist circuit is to be run in 16mm SWA to the sheds cu. Is it acceptable to use a two pole MCB instead of a KMF to protect the SWA. Do people tend to opt for a KMF because that was the norm before MCBs become widely available, or do KMF fuses offer higher max Zs to meet dissconection times. Thanks
Using a KMF will provide better discrimination. Having 60898 circuit breakers in series will not provide discrimination. However a KMF may fall foul of regulation 421.1.201 and be classed as similar switch gear. So you would have to house the KMF in a non combustible enclosure which isn't ideal or use something like this Wylex switch fuse. https://www.amazon.co.uk/Wylex-DSF100M-Amendment-Single-Cartridge/dp/B01E3X1QE8 out of interest what is the existing CU?
These switch fuses are generally referred to as a KMF. KMF was/is a part number for a MEM switch fuse like this but the name has kind of stuck for switch fuses of these types even though other manufacturers make ones that are very similar such as wylex, click etc.
Because depending on manufacturer, existing load, load of the new distribution circuit and a few other factors then you may of been able to use a fuse carrier in the existing board like this https://www.bing.com/images/search?q=hager+fuse+carrier&FORM=HDRSC2
Another point is you will never be able to gland an SWA in to a KMF so you would have to use an adaptable box or something similar which IMO is a bit of a PITA.
The links not working for me there but thanks anyhow; the existing CU is a domestic type, 10 way and without any spare ways, a submain from this would overload it I expect !
I would opt for the new Wylex switch fuse too. The new ones have a metal fuse cover.... You would have to gland your SWA into an enclosure before the KMF, so a metal clad switch fuse is the way to go. I tend to use the gland set TRS gland for the tails, even though not particularly required, and intended for TT installs. Keeps things neat.
I've been using these http://remora.net/catalogue/nylon-c...ail-Kits/GripLoc-Consumer-Unit-Tail-Kit-Nylon I've been getting them from KEW electrical supplies for about 10pence more than what's advertised on remoras site but don't have to pay the postage. Cheaper than Wiskas equivalent.
This situation has nothing to do with discrimination between disconnection devices. The OP is a muddled question, tbh. A KMF is a fused switch which simply has a fuse in the phase side. There is no reason you could not adopt a double pole mcb arrangement if you wanted to or take a new circuit off the existing CU if this was practical. A 60A or 80A BS1361 will not discriminate with the main cut-out. But the question you need to ask yourself is are you really that concerned that the load from a shed would come close to overloading a 16mm2 SWA? There is really no need to put any fused device on the front end as the main cut-out will be there exactly as it would if you were coming directly off the CU.
Lee means discrimination between downstream MCBs and the protecting MCB. During a fault of high fault current, you cannot guarantee which MCB would operate, it could be the 32amp in the subboard or the 63 protecting the submain. With a fuse, you have discrimination between the submain and subboard. It is not uncommon to see a fault a on a small sub circuit take out an MCB protecting a submain. We don't know what is in the shed, but we must assume it's more than just a shed if 16mm and a KMF were to be used.
The dist circuit swa needs to be protected by something other than the main cut-out, which is the gist of the post; ??
No it doesn't. That's the point of my reply. All the fuses will be in the shed end protecting the SWA. What is the point in putting a device between the SWA and the cut-out? No discrimination is available and it is unnecessary.
Isolation unphased, and the tabulated cc may need a lower rating device than the 100 a main switch. Im not to rely on the main cut out for a dist circuit, the whole place would be in the dark if someone cut throgh the swa, are you sure about what your proposing ?