Hi Can someone confirm wether a lighting circuit has to disconnect within .4sec when on a TN system.The lighting cct is to be on a 6amp cb protected by a 30ma rcd. thanks.
Blimey that £300 i paid for my 17th update course last month must of been worth it as i knew the answer.
Any circuit subject to a fault on a RCD will disconnect within the tripping time of the RCD surely?..So this makes some values immaterial?..although can see that as long as you are below the requieste times, then I suppose what I say is irrelevant with respect to this.
on TT it is 0.2, if you have main bonding on services you can use 0.4s ----------------------------- I think you've misunderstood something there Gary, where would you have a TT system that didn't have main bonding to services?
In the regs it says if you have main bonding conductors to incoming services then you can use the TN system 0.4s disconnection times. page 46 main regs book
Thanks Sen..about time I started studying up a bit really..its not the sort of game where guessing at stuff is relevant really. Anyway thanks again Sen, and have a good evening M8.
page 46 main regs book ------------- This is talking about bonding connecting all extraneous conductive parts of the location, eg supplementary bonding, not main bonding. As supplementary bonding isn't always necessary in 17th due to rcd protection etc the max disconnection time is 0.2 seconds.
Has anyone here actually tried witnessing such a fault whilst in possession of a Swiss-made stopwatch? Lucia x
Thanks for the help.I had found it in the regs but was a little unsure if there was another trick answer. summit.