Have chased cables in and gone to connect down to the consumer board below. The board sits with a joist running above it. Awkward now getting a cable through. Can I enter the board from the side and put some trunking there. I presume that is ok? Also the radial will only be supplying four sockets. TV sky alarm clock! Would best practice be 16amp? Any thoughts would be helpful.
Feed it into any position you like, top, bottom side or rear. No need for gland if it's t/e, personally I often use closed grommets with a suitable sized hole as the open ones do tend to leave a rather large gap around the cable.
20amp would be more expected. I don't know what this fascination with 16 amp radials is. I'm sure you come in from above if you try.
Hi lec. Is it a historical thing perhaps - from the 15A re-wireable radial? Seems daft thou on a cable rated for 26A
Yeah, 16A is good, but 32A is better. Loads of power AND the hot cables will heat your house. MASSIVE bonus mate!
Standard socket circuits. A1 - Ring - 32amp - 100m/sq A2 - Radial - 32amp - 75m/sq A3 - Radial - 20amp - 50m/sq Why use a 16amp when a 20amp would be perfectly fine and expected? You don't put a 25amp on a ring "because it's plenty".
Yes I've found that to be the case too Peter, never had any problems with the 16a circuit's I've installed.
I don't see the fascination with the 20A circuit breaker on a radial......If the design current of the circuit allows for a 16A circuit breaker then a 16A circuit breaker is fine.
How can you be sure of a design current for socket circuit? You should be providing as much as the circuit will allow. Pointless not to.
I've installed countless 16A radials at not once had to go back and swap it for a 20A circuit breaker.....What do you think the likely hood of a 16A radial with four sockets that you've designed/installed for a TV, sky box and alarm clock tripping due to over load is?
No I wouldn't as to allow a little more scope for additional/unexpected equipment to be plugged in. I very much doubt my entire house pulls 16A most of the time let alone a radial with four sockets on it.