Radial circuit

Discussion in 'Electricians' Talk' started by tore81, Jul 30, 2016.

  1. tore81

    tore81 Screwfix Select

    Have chased cables in and gone to connect down to the consumer board below.

    The board sits with a joist running above it. Awkward now getting a cable through.

    Can I enter the board from the side and put some trunking there. I presume that is ok?

    Also the radial will only be supplying four sockets. TV sky alarm clock! Would best practice be 16amp?

    Any thoughts would be helpful.
     
  2. Sparkielev

    Sparkielev Screwfix Select

    Is it a metal board if so use 20mm gland
     
  3. seneca

    seneca Screwfix Select

    Feed it into any position you like, top, bottom side or rear. No need for gland if it's t/e, personally I often use closed grommets with a suitable sized hole as the open ones do tend to leave a rather large gap around the cable.
     
    tore81 and FatHands like this.
  4. nigel willson

    nigel willson Screwfix Select

    New circuit!!! no testing , building regs ect!!!????
     
  5. Rulland

    Rulland Screwfix Select

    With respect Nigel, tore was asking about entry to board, nothing more.
     
    tore81 likes this.
  6. Lectrician

    Lectrician Screwfix Select

    20amp would be more expected. I don't know what this fascination with 16 amp radials is.

    I'm sure you come in from above if you try.
     
  7. JP.

    JP. Screwfix Select

    I sometimes use a 16 amp mcb on a 2.5 radial final Lec - even though a 20 amper is more the norm..:)
     
    tore81 likes this.
  8. FatHands

    FatHands Well-Known Member

    Hi lec. Is it a historical thing perhaps - from the 15A re-wireable radial? Seems daft thou on a cable rated for 26A
     
  9. Billy Towler

    Billy Towler New Member

    Yeah, 16A is good, but 32A is better. Loads of power AND the hot cables will heat your house. MASSIVE bonus mate!
     
  10. tore81

    tore81 Screwfix Select

    character. Thank you for the replies
     
  11. Sparkielev

    Sparkielev Screwfix Select

    Yeah blind grommet far better option than a gland
     
  12. Lectrician

    Lectrician Screwfix Select

    Standard socket circuits.

    A1 - Ring - 32amp - 100m/sq
    A2 - Radial - 32amp - 75m/sq
    A3 - Radial - 20amp - 50m/sq

    Why use a 16amp when a 20amp would be perfectly fine and expected? You don't put a 25amp on a ring "because it's plenty".
     
    FatHands, tore81 and KIAB like this.
  13. peter palmer

    peter palmer Screwfix Select

    16A MCBs/RCBOs seem to be a lot more readily available then 20A ones.
     
    KIAB likes this.
  14. seneca

    seneca Screwfix Select

    Yes I've found that to be the case too Peter, never had any problems with the 16a circuit's I've installed.
     
  15. Lectrician

    Lectrician Screwfix Select

    I don't find that, wholesalers stock every flavour.
     
  16. leesparkykent

    leesparkykent Well-Known Member

    I don't see the fascination with the 20A circuit breaker on a radial......If the design current of the circuit allows for a 16A circuit breaker then a 16A circuit breaker is fine.
     
  17. Lectrician

    Lectrician Screwfix Select

    How can you be sure of a design current for socket circuit? You should be providing as much as the circuit will allow. Pointless not to.
     
  18. leesparkykent

    leesparkykent Well-Known Member

    I've installed countless 16A radials at not once had to go back and swap it for a 20A circuit breaker.....What do you think the likely hood of a 16A radial with four sockets that you've designed/installed for a TV, sky box and alarm clock tripping due to over load is?
     
  19. Lectrician

    Lectrician Screwfix Select

    Why not put a 6amp on it then? You wouldn't would you.
     
  20. leesparkykent

    leesparkykent Well-Known Member

    No I wouldn't as to allow a little more scope for additional/unexpected equipment to be plugged in.
    I very much doubt my entire house pulls 16A most of the time let alone a radial with four sockets on it. ;)
     