Glow worm Micron FF50 Boiler I previously posted question and now have all the parts etc so have described what I'm going to do (more for a sanity check) and will be wiring to my HVAC Wiring Centre, Honeywell 42005748-001 - http://uk.rs-online.com/web/p/hvac-wiring-centres/2001342/ and a couple of questions about links at the end Honeywell Cyl Stat - C,1,2 to Wiring centre C,1,2 Honeywell Thermostat - E, 1,2,3,4 - to wiring centre - E1,2,3 (no 4 in the centre) to just use the 3 Mid Pos Valvel - Grey, Blue, Orange, White to the same on the wiring centre (wiring center has a brown but Valve does not) Boiler just has E, N, L wires (as in the 3 of them) so in wiring center assume I just use L N and E Live feed is obvious Now we have the programmer which seems straight forward L, N, HW On, Hw Off, CH On - to its counterparts in the wiring centre So whats left ahh, which links to cut and here I get confused I think I use the Y plan (mid posn valves) so cut links L4 and L5 and I have read the boiler manual and it does not talk of pump overun anywhere so I guess I ignore that bit thanks in advance john B
Honeywell Cyl Stat - C,1,2 to Wiring centre C,1,2 Correct Honeywell Thermostat - E, 1,2,3,4 - to wiring centre - E1,2,3 (no 4 in the centre) to just use the 3 Correct; Terminal 4 is used for cooling applications Mid Pos Valvel - Grey, Blue, Orange, White to the same on the wiring centre (wiring center has a brown but Valve does not) Are you connecting to the correct terminal block? The mid-pos valve connects to the 6-terminal block on the right, below the pump block. The white terminal is the bottom one. Boiler just has E, N, L wires (as in the 3 of them) so in wiring center assume I just use L N and E Correct Live feed is obvious So it is L, N, HW On, Hw Off, CH On - to its counterparts in the wiring centre And so is this I think I use the Y plan (mid posn valves) so cut links L4 and L5 Correct and I have read the boiler manual and it does not talk of pump overun anywhere so I guess I ignore that bit Correct john B[/QUOTE]
Thanks for the response so my research has paid off (nearly) as for the query Mid Pos Vvalve- from the valve there is Grey, White, Orange, Blue and Earth (its a 5 core cable) there is no brown so they go to the corresponding place in the wiring terminal on the right below the pump - there just wont be a brown ? John B
Hi finally ready, just one more question about the Mid Posn Vave connection, the wiring center can accommodate up to 6 connections, my valve only has 5 wires - there is no brown - i assume this is not an issue ? Regards john Berman
Sorry I didn't reply to your last post. The lack of a brown is not important. Just wire the five wires according to colour to the appropriate terminal in the right hand valve terminal block.
so all connected but there is an issue, Hot water is fine, CH is not, when I turn up the thermostat I would expect the pump to start and the valve to move - neither of these things happen ? Are there any checks I can do to see where the issue is ? Regard John Berman