Solar PV system question

Discussion in 'Electricians' Talk' started by slapstyxx, Aug 3, 2016.

  1. slapstyxx

    slapstyxx Member

    Hi All,

    I'm seeking some advice about a solar PV system we had installed in November 2014 please. I would take it back to the contractor, but they've ceased trading, and it turns out that they never provided our details to the so-called insurance backed guarantee firm. That means we're tucked up a treat, but still paying for the privilege.

    They installed a 4kW system comprising 16 off 250W Canadian Solar panels. After 18 months, we seem to be consistently short of the predicted generation figures. That's when I discovered the installer had gone bust. The array is connected to an inverter made by SAJ, who've been quite helpful so far.They tell me the inverter is rated at 3kW, and that regardless of how much power the panels produce, the inverter will cap the output at 3kW. Is it normal practice to install a lower rated inverter than the max power that the panels could produce? Is that likely to be the reason our generation seems lower than we expected, or could it be a duff panel? And perhaps most important, is it safe?

    As far as I can tell, the output from the inverter is linked straight into a ring main. Is that good practice? The inverter log has collected a lot of error messages most of which are grid or isolation related. While SAJ say they'll help interpret those, is the way the system's connected to our mains a possible contributing factor to these errors?

    The only good news is that the finance provider says we can make a Section 75 claim to get it put right, if indeed it's wrong.

    I'll be really grateful for any advice.

    Many thanks in advance

    Mark
     
  2. peter palmer

    peter palmer Screwfix Select

    I cant offer any help, never done a solar install but there must be diagrams on line of how they are supposed to connect up.

    However I'm not in the least bit surprised that complaints like the above are beginning to surface. If something looks too good to be true..........
     
  3. Stugadget

    Stugadget Member

    Hi Mark,

    You can install a smaller Inverter than the array size as although you have a 4kW system there are not many times a year that it would actually be able to generate 4kW's. Having said that I would have installed one rated at 3.68 as a 3 kW one will de-rate itself a lot and should not have been installed. Over voltage will kill the inverter and I would have thought that if they had done that it would have died by now.

    Definitely should not be connected to ring main should be on own dedicated supply.

    Could be all sorts of reasons why it's not performing and I'm afraid the only way to tell is through testing the array voltages and current.

    Isolation errors are a bit worrying they usually mean that the DC side is making contact with earth this could be a loose connection getting wet or a cable that has been damaged.

    Where are you based ? I'll help you out if I can

    Stuart
     
  4. Mr. Handyandy

    Mr. Handyandy Screwfix Select

    If the installers have gone bust, who are you still paying?

    'Tis they you need to speak to.

    If the install company have failed in their duty (contract) you might be able to get the finance co to quash the loan and they would claim it from elsewhere.

    Mr. HandyAndy - Really
     
  5. Slap, that doesn't sound good... :oops:

    4kW fed directly into a ring main? Jeepers - surely that's very very wrong? And, whilst I understand it's good to select an inverter that's close to the output - driving it 'hard' makes it more efficient - a 3kW inverter on a 4kW array sounds nuts.

    But I dunno for sure.

    You need specialist advice from peeps who know all about these systems, and I'd recommend this site as the place to go to: http://www.electriciansforums.co.uk/forumdisplay.php?f=42&s=8a782f2c331b20a80f4ea76f5fff352b

    I'm sure they'll guide you. There are some cracking folk on there ('SolarCity' - Chris Hammond - for one), and these professionals hate cowboys even more than you do.

    Good luck - and please keep us posted on what happens.
     
  6. philthespark

    philthespark Active Member

    Unfortunately there are a lot of cowboys out there,I got involved with one about 18 months ago,I went to report on the electrics side and a solar guy reported on that side.It was a holy mess,ended up in a court case which last I heard was still going on,the installer had loads of ccj's against him and just kept closing down and opening up under another identity.In our particular case we even had evidence of him threatening the customer! She'd got in touch on another forum and a couple of us decided to help her.Unfortunately what we found was that the scheme he belonged to kept saying she had to give him a chance to put it right,first they gave him one chance,he did nothing,they gave him another,again nothing.Everyone she complained to said he had to be allowed time to put it right,a year later she was no further on and so there was the court case,again he was given the chance to make good,again he didn't,as I say I've no idea how or if it ever got resolved but I wasn't hopeful.
     
  7. Horrible tale, Phil.

    It certainly used to be that you'd need to give a person 3 chances to put things right, and I can understand the reasoning in allowing them at least once decent chance.

    However, I also understand that's changed now - certainly the 'three chances' bit - and if you can show good cause for not wanting the same person back (clear incompetence, not qualified, threatening behaviour, illegal activity, etc), then you don't even have to allow them one opportunity.
     
  8. Sparkielev

    Sparkielev Screwfix Select

    It disgraceful people paying hard earned money and these lowlifes getting away it the likes of niceic napit elecsa and others should hang there heads in shame for doing nothing to help customer and true sparks
     
  9. peter palmer

    peter palmer Screwfix Select

    That would mean doing something for the money we pay them, like everything else they are just greedy ********, in fact they are cowboys themselves.
     
  10. Sparkielev

    Sparkielev Screwfix Select

    True
     
  11. TheMorg

    TheMorg Active Member

    Out of interest, I assume the installer is still trading, just under a different name?
     
  12. philthespark

    philthespark Active Member

    I believe so,yes.
     
  13. slapstyxx

    slapstyxx Member

    Thank you for all your replies. I was trying to convince myself that it was just the changes to the FIT scheme that made trading too difficult for the installer, but it sounds as though we were well and truly had :(
    I guess alarm bells were ringing from Day 1. Their sales pitch said that they'd erect a scaffold. When they booked the job, they said the scaffolders would be in the day before. We rang them to say no one turned up, but they said it was all in hand. On the day, the installers turned up with a couple of ladders... My wife says their electrician spent only about 30 minutes here, and a big chunk of that time he was filling in an inspection report!

    Stugadget - Our CU has a number of spare ways on it, so they could have run a separate circuit back, but that would have involved laying cable all the way to the other end of the building! Since my original post I've traced their wiring. They brought a 2.5mm cable out from the inverter into a separate MCB on the shower CU. That's fed from the main CU by a 10mm cable, which sounds like overkill until I tell you it's a 10.8kW shower. On a sunny day, there's a steady red light on the main meter, which means we're generating more than we're using, but overall, we're about 8% lower than predicted. It's not huge, and I suppose it could be simply that it hasn't been the best summer so far. Perhaps another factor is that the roof faces southwest, and it's a very shallow pitch at 22.5 degrees, but surely that should have been taken into account in the original calculation? We're tucked away down in the southeast in Hythe, Kent.

    HandyAndy - The installation was financed through Barclays Partner Finance. I've been in touch, and they've already logged it as a potential Section 75 claim, whatever that is. They asked me to first ascertain whether there was any insurance, which seemed fair. It turns out that it was never logged with the insurance company, so it's back to Barclays. In fairness, they said they'll help me resolve the issue and that's one reason why I'm keen to gain as much insight as I can. My guess is that it will be a once only shot. If the panels are working OK and it just needs an uprated inverter, that might be the lowest cost solution for them. We're getting FIT payments and a fair amount of 'free' electricity, just not as much as we'd expected. On that basis, a reduction rather than a write off would be fair, although I won't complain if they decide to write it off.

    DA - That's a very useful link and I'll follow up there too, thank you. I agree that it sounds nuts, and that's what made me ask here. I'm glad it wasn't just me! I'll report back in due course with any more info.

    I've done some background checks and as far as I can see the installer has genuinely ceased trading. There's no sign yet of the directors popping up anywhere else; having said that, they only went down the tubes in April this year. If they reappear in this sector I may start asking some awkward questions very publicly.

    Thank you all again for your comments and advice

    Mark
     
  14. Keep us posted on this, please, Slaps - it's an interesting one :)

    And do join that forum and ask on there. The peeps on there are true pros and experts in this field.

    'SolarCity' on there is the company I went with for my install following help and guidance on that forum. They were everything you'd hope from a bona-fide company, and I know you'll only get sound advice from them.
     
  15. slapstyxx

    slapstyxx Member

    All,

    Reading back my last reply, I see I missed one other thing. The installers put the inverter in the loft. I'm not sure whether that's standard practice, but it seems odd given that the manufacturer gives very clear instructions about the importance of air circulation around the device. There's a whopping big heatsink on the back, which tells me that it generates heat as it converts DC into AC. The shallow pitch on our roof means there's not much space up there, and it gets unbearably hot in summer. Does that mean the inverter is under even greater stress?

    Thanks again gents

    Mark
     
  16. I think the loft is ok, Slaps, although as you say it can get very warm up there. Yes, inverters become warm when they're pushing it at max output - which is what you ideally want as they are more efficient.

    Anyhoo - ask them 'other' guys. You will get good answers :)
     
  17. Stugadget

    Stugadget Member

    Hi Mark,

    Based on a 3kW inverter you should be looking for around 3135 kWh's per year with about 363 kWh's this month.

    A 4kW system with the correct sized inverter should do 4180 kWh's per year.

    How is your system performing aginst my estimates ?

    Bet they haven't put a lockable isolator at the main C/U position or notified your local DNO.

    Loft is not ideal but o.k. However your inverter will be working hard which will shorten its life and I would have though SAJ will not replace it under warranty if they know how under dimensioned it is.

    upload_2016-8-7_20-4-28.png
     

    Attached Files:

  18. slapstyxx

    slapstyxx Member

    Hi Stuart

    Thank you again for your advice. I'm a little confused because the pre-sales estimate was 4020kW per year, which falls in between your two figures. Perhaps that's another sign they misled us.

    In actual performance terms we're seeing better than your estimate. We produced 3786kWh in the past year, which is 6% down on the sales prediction. In the last 30 days we produced 482kWh. Here's a summary in more detail: -
    output.png

    So, am I right in thinking we're actually doing better than we should be, given the constraints of the inverter, but not as well as we could be if a correctly rated unit had been installed? We're definitely down on what we expected.

    On your other points, there is a lockable isolator next to the generation meter, which is where they tapped into the shower CU, and there's a label by the main CU to alert anyone that there is a Solar PV installation. The shower circuit is protected by a 50A MCB and labeled "Shower/SolarPV". There are secondary MCBs in the shower CU, one for the shower & one for the Solar PV. The electrician gave us a NAPIT Electrical Certificate and a circuit diagram, and we have an MCS certificate, but I'm still uncertain whether the circuit was compromised by the addition of the Solar PV.

    There's no sign that they told the DNO. If I understand that term correctly, would that be UK Power Networks in my area? Should I advise them of the installation?

    SAJ tell me there's a networking facility on their inverter, which would make interrogating it simpler. It's a long way from my router so they're sending me details of how to connect via wifi. They seem very responsive and keen to help at the moment, but as you say, that may change if the unit fails because it's underrated.

    Thank you again

    Mark
     

    Attached Files:

  19. Slaps, go on to that other forum - these guys are experts in this field and will answer all your questions (not saying that Stug isn't, but that other forum is run by guys who 'do' PV every day).

    And then let us know what they say!

    (Fair chance that one will offer to come out and have a gander if they are close enough too...)
     
  20. Stugadget

    Stugadget Member

    Hi Mark,

    I think your systems doing ok but could do better with a larger inverter, the largest one you could install would be a 3.68 without preapproval of the DNO.

    I don't think it would be a good idea to contact the DNO it isn't your responsibility and if the original company didn't do it then there will be no come back on you.

    The electrical setup you describe isn't correct and could be dangerous. I guess there is an RCD somewhere in the shower circuit and the problem is the inverter only has to shut down within 5 seconds of a mains fail but an RCD should operate withing 40ms. So if there is a fault and the RCD trips the inverter could continue feeding in for a further few seconds thereby keeping the circuit live.

    What model SAJ Inverter has been installed ?

    DA I've been installing PV systems for over nine years and so I know what I'm talking about.
     