Hi folks, Am looking for a bit of advice, I have a small garage workshop which is attached to the side of our house, it has a ring main circuit from the house consumer unit, and the consumer unit has a rccb within 80 amp load and 100 mA trip , should I get an RCD on the garage circuit or is it OK as it is? I use normal wood working power tools in the garage.
If you're not planning to use any outdoor equipment and the sockets were installed before the 17th. edition came into force I would say don't bother with a 30 m/a. Of course if the sockets have been installed since 17th edition came into force then they should be 30m/a rcd protected.
There is a socket that we take power out into the garden, but was thinking of replacing it with a RCD 2 gang socket, I have extended the garage circuit since the 17th.
If you have installed any extra sockets, then they should have been provided with 30mA RCD protection.
No it isn't. There is no such thing as a fail. Satisfactory or unsatisfactory. He is putting an SRCD on so no problem anyway.
On an EICR (formally PIR), Absence of RCD protection for "portable or mobile equipment that may reasonably be expected to used outdoors" is recommended as a C2 code by the NIC. Absence of RCD protection to other sockets is recommended as a code C3. A report with any C1 or C2 items becomes "Unsatisfactory".
Confession time! As you guys would have gathered from my original post I am not a Sparky but a carpenter and did a bit of small scale electrics for customers until part P came in , now I just do stuff on my own house,(yes I know that it is now considered " illegal") I did buy the RCD all ready, but just wanted to check that I had to fit it, it is not called a SRCD though just an RCD . Ok here is the embarrassing bit, I don't know how to fit the RCD! I would probably get a sparkey in but my problem is that although I am pretty sure that the electrics are safe some of them may not all comply with all of the regulations and i dont want to fork out a whole heap of money or risk getting them failed. Perhaps i am being overly paranoid, and perhaps I will just fit the RCD myself once some nice sparkey has told me how to do it.