SWA cable rating and earthing

Discussion in 'Electricians' Talk' started by staresy, May 12, 2004.

  1. staresy

    staresy New Member

    What is the typical current rating of 2.5mm 3 core SWA some underground, some clipped in air.

    Also, do the regs stipulate that both ends of the armour are earthed?

    Ta
     
  2. ChubbyPhaseWire

    ChubbyPhaseWire New Member

    What is the typical current rating of 2.5mm 3 core
    SWA some underground, some clipped in air.Clipped in AIR?

    Also, do the regs stipulate that both ends of the
    armour are earthed? Not always ?

    Ta
     
  3. Lectrician

    Lectrician Screwfix Select

    You only need earth one end if you are using a seperate conductor for the 'real' earth. But sometimes just as easy to do both.

    Clipped direct to a surface in "'free air'", 2.5 will carry a max of 28amp single phase and 25amp 3phase.

    Underground you should allow the same.
     
  4. ChubbyPhaseWire

    ChubbyPhaseWire New Member

    What is the typical current rating of 2.5mm 3 core
    SWA some underground, some clipped in air.

    Also, do the regs stipulate that both ends of the
    armour are earthed?

    Cables exceeding 50mm may be bonded together at one point in their run.
     
  5. Lectrician

    Lectrician Screwfix Select

    you are thinking of singe cores there CPW
     
  6. ChubbyPhaseWire

    ChubbyPhaseWire New Member

    you are thinking of singe cores there CPW

    Well actually i was thinking about my cup final ticket.
    Have a look at 523-05-01 what do you think about?
     
  7. Lectrician

    Lectrician Screwfix Select

    Yea CPW, read 523-05-01, refers to SINGLE CORE ARMOURS.

    We installed 4 x 400mm Single Core Alumnium Armours for a gen set, this reg applied to us then. But more multicores, it doesnt apply.
     
  8. unphased

    unphased Screwfix Select

    What is the typical current rating of 2.5mm 3 core
    SWA some underground, some clipped in air.

    Also, do the regs stipulate that both ends of the
    armour are earthed?


    Table 4E4A. Ref method 1 31A, ref method 11 33A.

    The regs stipulate that you must have an earth SYSTEM Whats the point in earthing just one end. Where is the fault to earth going to?

    RSS
     
  9. Lectrician

    Lectrician Screwfix Select

    earth!

    Earth the supply end only if you are using a seperate core to earth the socket / garage at the end.

    Only one end needs earthing, most usually the supply end. Thats the end of it.
     