tripping RCD

Discussion in 'Electricians' Talk' started by cearnshaw, Mar 27, 2017.

  1. Joe95

    Joe95 Screwfix Select

    Do you mean......he should do the job properly?
     
  2. bright_Spark

    bright_Spark Screwfix Select

    I wonder if he has put the neutral to the lights to the non rcd side as well or left it?
     
    spen123 likes this.
  3. cearnshaw

    cearnshaw Member

    this was the kitchen circuit
     
  4. cearnshaw

    cearnshaw Member

    he did move a blue wire over
     
  5. Sparkielev

    Sparkielev Screwfix Select

    If it was me I wouldn't of left untill I was satisfied it was sorted
     
    spen123 and bright_Spark like this.
  6. cearnshaw

    cearnshaw Member

    he's back at 8am. So far he has called at the end of the day so I think/hope he's here for the duration tomorrow
     
  7. bright_Spark

    bright_Spark Screwfix Select

    same here, I wouldn't sleep
     
  8. Sparkielev

    Sparkielev Screwfix Select

    No point coming over moving a wire and hope for the best he can't know without testing that it fixed
     
    spen123 likes this.
  9. bright_Spark

    bright_Spark Screwfix Select

    Zs reading is on the high side but still a pass, I am sure it has to be something really stupid
     
  10. cearnshaw

    cearnshaw Member

    so before I attempt to sleep, kitchen MCB on or off?
     
  11. Sparkielev

    Sparkielev Screwfix Select

    I know you said it was difficult to run new circuits but this is why I try my hardest to run my own to avoid any grief
     
  12. bright_Spark

    bright_Spark Screwfix Select

    Probably wont need to it will do it itself!!!!
     
  13. cearnshaw

    cearnshaw Member

    Zs?
     
  14. bright_Spark

    bright_Spark Screwfix Select

    Yes the extra bit of work saves all of this
     
  15. bright_Spark

    bright_Spark Screwfix Select

    Earth loop
     
  16. bright_Spark

    bright_Spark Screwfix Select

    allowed 1.10 and this is a tns system so .80 is on the high side so it points to a leaking earth
     
  17. Sparkielev

    Sparkielev Screwfix Select

    R1 R2 is 1.97 which is high also
     
    spen123 likes this.
  18. cearnshaw

    cearnshaw Member

    so what does that mean?
     
  19. bright_Spark

    bright_Spark Screwfix Select

    yes and he has added sockets to this, I would definately have gone with a new circuit in this instance
     
  20. cearnshaw

    cearnshaw Member

    tested after sockets added
    So for a non-electrician what does that point to
     