ok removed ceiling pendant in a kitrchen and replaced with 4 downlighters . the existing circuit is none RCD protected. ive been informed by a certain techincal helpline the circuit now needs RCD protection, this is news to me as i have not installed the existing cables to switch ect just replaced lights
Agreed, RCDs are now required on domestic lighting circuits, if the circuit is modified (replacing the lights, which are fixed equipment counts as that) then it must be brought up to spec. If you have a modern type consumer unit you should be able to get an RCBo to fit for that circuit or move that circuit to the RCD protected side if there is space.
Just checking. Is this replacing the pendant with a light fitting that has 4 down lighters, or have you installed 4 separate down lighters?
it isnt just cables buried in a wall that require RCD protection. the regs now require light fittings in a domestic environment to also be RCD protected
Quite right ,but the regs are not retrospective ,and if all that the op has done is changed a light fitting ,there is no requirement to now upgrade the circuits protection with an RCD.
Has he though ? That's why Spinlondon has asked the question. Let's face it ,it wouldn't be the first time that a diyer had used the wrong terminology.
im pretty sure thats what hes done. “removed ceiling pendant in a kitrchen and replaced with 4 downlighters‘’
I agree with previous responses. If the question is about how do I bring my house lighting circuit up to current standards having adapted one of them then yes, you have the answers above. Interestingly tho, for the sake of argument, If you had kept your pendant and instead of putting a lamp in it, you put a surface extension lead with 4 surface downlighters daisy chained, (LED lamps so less load than original) then strictly speaking you haven't changed any fixed wiring and therefore the new regs wouldn't necessarily apply. Yes, I know it's a dumb analogy but Just pointing out that sometimes doing a decent job brings on additional requirements, whereas a DIY bodge wouldn't do! Crazy world we live in.. but safety first?
A mate of mine has just installed quite a few led downlighters (with my help), there is no rcd protection at the consumer unit. Although there are no "new circuits" involved the fact that we have added to the existing circuits means that rcd protection should be provided to comply with 18th.regs. As i'm no longer a scam member I can't do a c/unit change for him so i'm thinking of fitting a "front end" 30m/a rcd.
I would not recommend front end rcd as it is only a few lights and not outdoor socket or bathroom special location I would wait till you are ready to ns tall new consumer unit or just install a metal housed stand alone rcd just lighting circuits making circuit a lot safer