  1. Coloumb replied to the thread 'Making up' a cooker unit from 45A switch and 13A socket..

    Supplies to fixed equipment can also still be 5s, if you can wangle it to fit a fuse and no rcd. Who would do that these days?

    Mar 18, 2019 at 11:56 PM
  2. Coloumb replied to the thread 'Making up' a cooker unit from 45A switch and 13A socket..

    ^not a problem 4 me mate:)

    Mar 18, 2019 at 4:58 PM
  3. Coloumb replied to the thread 'Making up' a cooker unit from 45A switch and 13A socket..

    I don't think your allowed to fit a socket to a ctt. with a 5s disconnection time, usually a distribution ctt. using a fuse rather than...

    Mar 18, 2019 at 4:46 PM
  4. Coloumb replied to the thread 'Making up' a cooker unit from 45A switch and 13A socket..

    I'm pretty sure that's like a "best practice" sort of thing from the OSG. No actual reg, but I would have to check. Maybe someone here...

    Mar 18, 2019 at 4:32 PM
  5. Coloumb replied to the thread 'Making up' a cooker unit from 45A switch and 13A socket..

    The idea is the 2.5mm only carries the current needed for the plug so will not need overload protection. Fault current protection...

    Mar 18, 2019 at 4:03 PM
  6. Coloumb replied to the thread Is it Friday yet?.

    Is it Friday yet?

    Mar 18, 2019 at 11:33 AM
  7. Coloumb replied to the thread Supply upgrade advice (25Amp>32Amp).

    The 2.5mm cable CSA is too small for a 32a breaker. You would need to run in a bigger cable for this to work. A 25a fuse (I assume?)...

    Mar 18, 2019 at 11:23 AM
  8. Coloumb replied to the thread R1+R2 reading.

    Not done this sort of thing for ages... 2.5 = 7.41 mohm/m x 4 = 29.64 29.64 x 2 = 59.28 mohm r1 + r2 = 0.06ohm

    Mar 16, 2019 at 8:46 PM