Earth leakage

Discussion in 'Electricians' Talk' started by shocker, Apr 8, 2019.

  1. shocker

    shocker Member

    Debate at work...what code would you give a earth leakage switch as main isolator in domestic property
     
  2. Coloumb

    Coloumb Screwfix Select

    Would such a situation exists? I thought an isolator on a CU had been mandatory for years now.
     
  3. seneca

    seneca Screwfix Select

    I can only assume the op is talking about a front end rcd? The c/unit would have a main switch, if this is the case I don't see any code necessary.
     
  4. JC2779

    JC2779 Member

    Its not exactly a lot of info on which to make a decision. If your talking about a 30ma RCD covering the whole board then only a C3 as a recommended improvement. you still find in older TT installations there may be a 100mA RCD as a main switch covering the lights ect, then a 30ma for the sockets even then just a C3 as long as they still trip.
     
  5. Woloumbo

    Woloumbo Active Member

    If youre talking about an old voltage operated elcb,and its the sole protection on a TT supply,then it needs rectifying with haste. C2
     
    nigel willson likes this.
  6. Lucky13

    Lucky13 Member

    I tend to agree, but NICEIC says C3 unless the test button doesn’t work then a C2
     

    Attached Files:

  7. Bazza

    Bazza Screwfix Select

    If it’s a 30mA RCD then C3. It breaks the reg regarding splitting of circuits- single point of failure. But then a dual RCD CU has that feature as well!!
     
  8. nigel willson

    nigel willson Screwfix Select

    Would suggest he may be on about an old voltage trip. We need a pic I think
     