Been to Napit 17th Ed Seminar today-[b]Interesting!!!!![/b]

Discussion in 'Electricians' Talk' started by 2 wheeled ant, Jan 10, 2008.

  1. 2 wheeled ant

    2 wheeled ant New Member

    Any existing (unknown!) or new cable buried less than 50mm (if poss)has to be protected by RCD
    Taking into account if you chase both sides of the wall if possible! you can contravine building regs to structure.

    You cant convert an existing split board (take out ex dp switch & replace with rcd, as you cant have 1 feeding another or reconfiqure wiring so you loop from 1 rcd to another so they are independant, still need 1 form of isolation, put dp switch in seperate enclosure you say! nope cant do that as you have now altered board & manufacturers warantee

    Basically
    <u>TT</u>100ma RCD feeding RCBOs & 30ma RCD feeding MCbs or all Rcbos
    <u>Tns, Tcns</u>
    All rcbos
    Touch a circuit fit an Rcbo

    Ant
     
  2. Lokkars Daisy

    Lokkars Daisy New Member

    ********! what piffle! where you been Ant ?
     
  3. 2 wheeled ant

    2 wheeled ant New Member

    Newcastle football club
    A seminar with Napit & megger, tonight just got back


    Ant
     
  4. Lokkars Daisy

    Lokkars Daisy New Member

    No I meant where have you been of late ,haven't seen you post for months ..
     
  5. sinewave

    sinewave Screwfix Select

    How much U had to drink today young Ant? ;)
     
  6. Lokkars Daisy

    Lokkars Daisy New Member

    still need 1 form of isolation, put dp switch in seperate enclosure you say! nope cant do that as you have now altered board & manufacturers warantee

    but that really is **** NAPIT ! :^O
     
  7. *welsh.wizard*

    *welsh.wizard* New Member

    Never mind that Ant, This is where you should be.
     
  8. Ripped Off

    Ripped Off New Member

    Never mind that Ant,
    This is where you should be.

    Time for SF admin to pop up
     
  9. 2 wheeled ant

    2 wheeled ant New Member

    Haha nothing to drink yet!

    Just been busy making a living, not easy on your own!


    Ant
     
  10. 2 wheeled ant

    2 wheeled ant New Member

    still need 1 form of isolation, put dp switch in
    seperate enclosure you say! nope cant do that as you
    have now altered board & manufacturers warantee


    but that really is **** NAPIT ! :^O

    Yea i know! If you alter the original board your not insured basically!


    Ant
     
  11. 2 wheeled ant

    2 wheeled ant New Member

    Oh & ive been reading posts just have not replied due to laughter!



    Ant
     
  12. *welsh.wizard*

    *welsh.wizard* New Member

    I trust that RO & Ant Won't registering then.
     
  13. 2 wheeled ant

    2 wheeled ant New Member

    Only option to rcds is to put cables in metal conduit (metal/pvc capping not good enough)


    Ant
     
  14. Clark Kent

    Clark Kent New Member

    Oh & ive been reading posts just have not replied due
    to laughter!



    Ant



     
  15. 2 wheeled ant

    2 wheeled ant New Member

    I trust that RO & Ant Won't registering then.


    I will !!!! compared to Nics (ok i worked for other people then & not myself) i think they are good!


    Ant
     
  16. lumingo

    lumingo New Member

    split load

    rcbo the lights

    put everything else on the rcd

    why fuss?
     
  17. Lokkars Daisy

    Lokkars Daisy New Member

    still need 1 form of isolation, put dp switch
    in
    [/i]seperate enclosure you say! nope cant do that as
    you
    have now altered board & manufacturers
    warantee


    but that really is **** NAPIT ! :^O


    Yea i know! If you alter the original board your not
    insured basically!
    >

    Ant

    Not insurerd for what Ant !? You can buy mcb s main switches ,rcd s etc by themselves If we were to replace say an MK mainswitch with a Wylex mainswitch would I become uninsured ?

    also 1 form of isolation ? do you mean one point of isolation ? because that requirement does not exist!
     