63A breaker cable sizes

Discussion in 'Electricians' Talk' started by sillybillybob, Apr 26, 2010.

  1. sillybillybob

    sillybillybob New Member

    Hi fella's need just a wee bit of advice. What is the minimum size cable i can use for a 63A MCB, Type C. The isolator it is feeding is only 3 metres away from the distribution board. It will be a 3 core SWA clipped to a tray. Any help would be ok.
     
  2. wklivesvtime

    wklivesvtime New Member

    what do you think me old sponge bob
     
  3. spark&half

    spark&half Active Member

    10mm but many other factors have to be considered...


    ;)
     
  4. wklivesvtime

    wklivesvtime New Member

    bit tight that get a 16in you tight feker
     
  5. wklivesvtime

    wklivesvtime New Member

    what is it feeding 3p motor or a dist cct or summit else
     
  6. wklivesvtime

    wklivesvtime New Member

    for the sake of 3m your not gonna be breaking the bank any way what ever you slam in
     
  7. spark&half

    spark&half Active Member

    10mm xlpe can be good for around 90A if needs must..

    ;)
     
  8. spark&half

    spark&half Active Member

    I would bung in 16mm for the sake of a few pennies..

    ;)
     
  9. wklivesvtime

    wklivesvtime New Member

    kinell. Never slung a 10 in for a 90 load before, you laying it in a bed of dry ice
     
  10. spark&half

    spark&half Active Member

    Me neither..

    But I would have no problem installing it for a 63A supply if needs must..

    Depends what it was actually feeding, I mean if it was running at 60 odd amps all day long then 16mm it would be, but for say a submain with a few circuits getting used occasionally then 10mm will be fine.
    ;)
     
  11. sillybillybob

    sillybillybob New Member

    It running a Fork lift truck charger. the cable fitted to the charger is only 6mm. thats why i asked about the cable size.
     
  12. spark&half

    spark&half Active Member

    Are you sure it needs a 63 amp supply then?
     
  13. Home Farm

    Home Farm New Member

    Fork truck charges can have horrendous starting currents for the first few minutes on a flat battery.

    We always fit type D MCBs to big transformers like this.

    For the length involved I would have thought 16mm as a minimum. Labour costs will be 10 times materials.
     
  14. sillybillybob

    sillybillybob New Member

    i've passed on the job. customer refused to to accept that the supply/isolator and circuit breaker needed up grading. so they are going to get someone in (Jam roll!!!!) who will diconnect the current charger. and connect up the new chargers..... to A 20 supply !!!. the label on the side of the new charger states 80A

    oh well good luck to them.
     
  15. sillybillybob

    sillybillybob New Member

    he had the nerve to suggest i was INVENTING work for myself.!!!!!!
     
  16. The Trician

    The Trician New Member

    80A is probably the OUTPUT ELV SIDE of the transformer..........
     
  17. fooman

    fooman New Member

    yep proberly done yourself out of a job :(
     
  18. Lectrician

    Lectrician Screwfix Select

    Fork truck chargers come in many different sizes.

    20amp SP are common, as are 32amp TP. Not seen a 63 or 80amp SP TBH, I guess they could exist.
     
  19. Lectrician

    Lectrician Screwfix Select

  20. wklivesvtime

    wklivesvtime New Member

    yep proberly done yourself out of a job :(

    Too late for that by the sound of it
     