2 feeds off 60amp for Kitchen
Discussion in 'Electricians' Talk' started by Kiev, Sep 15, 2020.
  1. Kiev
    Kiev New Member
    Hello,
    Can I have some advice please?
    I'm replacing a big old ****-off Rangemaster oven, which runs off it's own 60amp feed, with the following:
    2 x 3.6 kw Ovens
    1 x 7.4 Induction hob
    All 3 items need to be hardwired. At the moment, there is a nice big rotary isolator in between the 60amp box and the cooker.
    My questions is:
    Can I simply put in a junction box after the isolator and split the feed to 3 Cooker Outlet Plates - 1 double for the 2 ovens and 1 single for the hob?
    Thanks
  2. nigel willson
    nigel willson Screwfix Select
    Would say no. Cables feeding said appliances would require 16mm cable . Put in small consumer unit fuse down ect ect
    Kiev likes this.
  3. spirits are real 2016
    spirits are real 2016 Screwfix Select
    What size is the cable supplying the range at the moment..
    Kiev likes this.
  4. Kiev
    Kiev New Member
    Big.
    Given the size of the cable insulation, I would assume it's 16mm
  5. unphased
    unphased Screwfix Select
    My thoughts are, as its such a hefty supply, and you have a decent size cable, you can very easily run all three appliances off the circuit. You would struggle to find a junction box rated at 60A so my suggestion would be to install a dual cooker outlet plate and connect that to the 16mm2 T&E and then wire off that in 6mm2 T&E to a single cooker outlet next to it. Wire the two ovens off the dual outlet and the hob off the single.
    Kiev likes this.
  6. Kiev
    Kiev New Member
  7. Bazza
    Bazza Screwfix Select
    Kiev likes this.
  8. Coloumb
    Coloumb Screwfix Select
    I'm not convinced 6mm on a 60a fuse is workable. 2.5mm cpc size will most likely be too small.
  9. unphased
    Fixed load situation, Ben. It's probably the physical connection of 3 x 6 in the terminal that will be a challenge.
  10. Coloumb
    It's not the load current it's the fault current.
  11. unphased
    Fault current will be the same irrespective of the cable size. Its more an overload problem. The cable won't overload because the load is fixed. Short-circuit would easily pop the 60A breaker.
    sparko69 likes this.
  12. Coloumb
    The short ctt. will for sure pop the breaker but the let through energy of a 60 a breaker, I would imagine, would be more than the 2.5mm cpc is designed for.
  13. unphased
    That's a fair point. I wouldn't know for sure without doing calcs.
  14. metrokitchens
    metrokitchens Screwfix Select
    Henley blocks and use singles all 6mm in trunking?
    Just a ‘kitchen fitters’ thoughts.
  15. unphased
    Hmm, not a bad idea metro.
  16. metrokitchens
    Cheers. When the cables are bigger than the pipes I ain’t gonna touch it :)
  17. Bazza
    Henley block is designed for “double insulated” cables like meter tails.
    We don’t know what sort of cable is envisaged. You cannot connect T&E to a Henley block in a compliant way, because the outer sheath must be inside the enclosure where the joint is made.
  18. unphased
    Good point Bazza. Didn't think that through. :rolleyes:
  19. metrokitchens
    I did consider that issue hence the trunking idea. Perhaps put the Henley blocks in an enclosure..
    Or just use three of the metal connector blocks, often used for main bonding, fixed in an adaptable box.
    16mm in one entry and three sets of 6mm singles exiting via round conduit.
  20. unphased
    Or maybe enclose the Henley inside a box? Take the cables in through glands. It could be designed with thought.