    I recently changed a consumer unit in a property and I moved some internal wiring as I was happy with the order of circuits on the split load board

    I’m paranoid that I put a 2.5mm ring main in a 40amp breaker can someone put my mind at rest and let me know that the wiring will be okay for a day until I can get over and change the breaker the next day
     
  2. spirits are real 2016

    spirits are real 2016 Screwfix Select

    Yes relax it will be fine for a day 2.5 is rated at 26 amp radial so 2 x 26 is 52 on a ring so well under the limit till you change it over..
     
    Powerelec likes this.
  3. Powerelec

    Powerelec Member

    doubt they will max it out over night you have to have several electric heaters on, which I doubt in this weather
     
  4. Ind spark

    Ind spark Screwfix Select

    Ring mains are left on 40 amps for years sometimes i don't think a night will matter.
     