There is a lot of hot air on this thread. Firstly, the pipe sizes must be calculated. The 42CD! consumes 4.4 cu Metres gas per hour. Look at the tables in the link. 9 meters of straight 22mm pipe gives 4.6 cu m/hr. I think there is more than 10 meters of pipe when it is all measured, back to the wall from meter etc is never taken into account. It looks like borderline case.
http://www.cda.org.uk/megab2/build/pub124/sec3.htm
The link above tell you how to size up the supply.
Points;
* A 28mm meter outlet connector should be used. Many keep the existing 22mm connector and connect the 28mm pipe to this. Must 28mm right to meter union.
From
http://www.bes.co.uk
Part No. 0246 plus a new washer.
* The gas fire rightly is teed off the 28mm pipe at the
* The hob requires its own gas supply right back to the meter outlet teed into the 28mm pipe. The boiler requires its own <u>dedicated</u> gas supply. In theory if the pipes are sized properly you can tee off the hob at the boiler. In practice surge at switch on can cause problems, especialy with a boioer with a high gas rate.
1. I would get them to make sure a 28mm meter connector is at the meter outlet.
2. Take the hobs gas supply right back to the meter.
3. Get them to put 28mm right through the roof void. One three metre length may do it
If problems after all this see National Grid, as it may be an undersized maintap with a 3/4" flexible inlet. Sometimes if the flexible inlet is bent too tight, very common, restrictions in supply can occur.