HI, just moved into a new house and it has a great workshop in the garden. Previous owner said it is supplied from the house approx. 60mtr by 4mmm and 2.5mm swa BUT 4 small lighting circuits(2 inside ligting/2 outside) are on 1 20 amp mcb back in the house and if ever it trips all the lights in the workshop can go out. Question.Can a breaker ie an MCB be fitted on each of the 4 circuits to stop this happening ie on the each light cable. Is this an 'inline rroduct@ or is it simply getting an electrician to fita small consumer unit with 4 mcb's-dont know if an RCBO is needed as the consumer unit back in the house has one?
The answer is yes but. Depending on what is causing the trip there may not be any/much fault discrimination between a lower rated MCB in the garage and the 20A MCB in the house. They will both see the same fault current flowing at the same time. A LED emergency light in the garage is a good idea if the tripping is causing a problem it will come on if the power fails. They are about £12 each depending where you get them from.
Thanks mate-I don't think it trips all the time,just occasionally if a bulb blows-so no RCBO needed? -just correct rated mcb's in a unpopulated box wiring incoming and outgoing neutral to neutral bar and both live connections in the mcb? ie incoming/ougoing?