I would run a 10mm cable from the new switch position to the shower. If in the future you put in a bigger shower you will only need to rewire to the switch.
I can see your point. However, there are other considerations required. A guesstimate doesn't always work.
For instance, 10500 watts @ 230 volts = 45.6 amps. Using Ref Method C, a 6mm T&E cable is big enough.
or
10500 watts @ 230 volts = 45.6 amps. Using Ref Method 103#, a 16mm T&E is not big enough.
All this information comes from Appendix 4 which is informative only, not a regulation. A nice mix of engineering judgement (ie is the shower going to be continually in use) with a dash of Appendix 4 will give the correct answer.
With this in mind, a 6mm cable will be big enough for a lot of installations concerning 10 kw or even 10.5 kw showers with a 45 amp breaker. Obviously, this will depend on the supply voltage.
6mm is also okay, volt drop wise, for a 25+ metre cable run @ 45 amps.