another oven hob question

Discussion in 'Electricians' Talk' started by Longee, Nov 9, 2010.

  1. Longee

    Longee New Member

    Hi,

    Hob 7.5kw 16 and double oven 4.6kw (52ish amps)both supplied from 6mm from cu (8 metre cliprd direct) to cooker 45amp cooker switch without socket and then this feeds ccu and from here two supplies one to each.

    With diversity this works out at around 23amps combined or 29amps seperately and this is on a 30amp mcb.


    Normally i would supply both appliances seperately (although this is a recent change as years gone by would have had no problem with this).

    Question is would you be happy to wire the hob and oven in to the existing supply?
     
  2. sinewave

    sinewave Screwfix Select

    Owt up to 15kW is OK on a reasonable short 6mm 32A MCB


    Check out Coooooookers in the OSG! ;)
     
  3. Longee

    Longee New Member

    Yep aware of OSG page 160 i think? but question was would you be happy doing it?
     
  4. Longee

    Longee New Member

    Anyone????????????
     
  5. seneca2

    seneca2 New Member

    I'd do it for a distance up to about 10m, more than that i'd think again.
     
  6. Longee

    Longee New Member

    Thanks Sen,

    Care to elaborate on why 10m and perhaps your maths behind your decision?
     
  7. sinewave

    sinewave Screwfix Select

    I would be Longlee if length is under 12-15M with no insulation.


    Having said that when I wired our Gaff I ran a 12 metre 10mm supply to run This even though max loading is 14.6kW, but if 6mm was already in then it would've ben fine.
     
  8. Longee

    Longee New Member

    Thanks Sine,

    That's a lovely cooker - i have a classic 110 but gas.
     
  9. fooman

    fooman New Member

    cheap tat then sinewave ;)
     