Builders & cable

Discussion in 'Electricians' Talk' started by refurb, Sep 12, 2007.

  1. refurb

    refurb New Member

    Hi
    The builder who is building the dwarf wall for my replacement conservatory had put 2 lots of 1.5mm T & E cable inside the cavity wall with 50mm kingspan on top. When I asked him if this was ok he said he was doing it to save time for the sparkie. The cable is for another single socket running from an existing socket. Would 2 lots of 1.5mm be okay & is it ok to run it in the cavity laid on the dpc under the kingspan? The run is about 2 metres.
    Thanks
     
  2. sinewave

    sinewave Screwfix Select

    Cables should not be run in Cavity and 2.5mm is the minimum size to use.
     
  3. edward current

    edward current Active Member

    u sure its 1.5mm......... 2.5 would make more sence for s/os
     
  4. ProDave

    ProDave New Member

    and there are derating issues if it's sandwiched between the DPC and a layer of kingspan.
     
  5. edward current

    edward current Active Member

    Cables should not be run in Cavity and 2.5mm is the
    minimum size to use.

    unless in coduit
     
  6. sinewave

    sinewave Screwfix Select

    > unless in coduit

    We're talking a 'Builder' here DD! ;)
     
  7. refurb

    refurb New Member

    It's 1.5mm not 2.5mm, but he has put in 2 cables, not sure about the conduit, probably not, is the cable in the cavity a fire risk with the kingspan on top?

    I best tell him to cut it & let the sparkie do it on the inside of the internal wall, the plasterer will get over it?
    Thanks everybody for your help
     