  1. ZS73

    ZS73 New Member

    I'd really appreciate advice on this ...
    Baxi 105e been heating house when hot water on over last few months so aware diverter prob (diaphragm?). Advised by heating engineer doing our service to hold off if it wasn't bothering us??
    Over the last week could only get hot water if I powered heating on first and now nothing will power up. It's trying but not firing up and getting flashing alert for fan.
    Went to get diverter service kit from two places (both out of stock) but completely conflicting advice from both places and two central heating engineers I've called earlier. Last one told me it's a different diaphragm than I went for and that there are two diverters on a baxi (neither have seen boiler this was over phone and given the full history as above). He said go straight for full diverter change at £250.
    It's a bit of a minefield as need to watch pennies so trying to try and find most likely root of problem to go for first in hopes this will sort it.
    Really appreciative for any advice.
     
  2. kiaora

    kiaora Well-Known Member

    Hi
    The basic test, is to see if the pin comes out and actuates the micro switch, it’s that sw. That fires the Boiler,

    If you can poke a small screwdriver or similar and operate the micro sw. Then see if it fires the boiler?

    Regards
    Peter
     
  3. kiaora

    kiaora Well-Known Member

    Ps,
    Don’t get confused with the pump proving sw, ?
    The top micro switch is pump proving, the end one proves the valve has gone to hot water,

    Regards
    Peter
     
  4. kiaora

    kiaora Well-Known Member

    If the end pin is not coming out, (with hot tap on of course)
    You need a service kit to refurbish the valve