DNO ?

Discussion in 'Electricians' Talk' started by madmaz, Feb 11, 2010.

  1. madmaz

    madmaz New Member

    Installing a new storage heating system will be pulling 64Amps full tilt however i couldn't determine the main fuse size no markings on it can you just ring the DNO and ask them ? or is this an unrealistic request ?? if it was say 60 Amps can i ask them to upgrade to 80A does this cost ?

    Many thanks

    MM
     
  2. sparky Si-Fi

    sparky Si-Fi Screwfix Select

    Ask them to contact their supplier to get the incomer uprated

    Then stay the * out the way!

    [Edited by: admin]
     
  3. sparky Si-Fi

    sparky Si-Fi Screwfix Select

    . . . .and there is a cost.

    Every supplier is different
     
  4. sysparks

    sysparks New Member

    Couldnt you pull it and hav look?
     
  5. seneca2

    seneca2 New Member

    I'm sure there's no seal on it!
     
  6. Removed 4

    Removed 4 New Member

    I can't see why you're worrying about this MM. You seem to have an off-peak load of around 15kW, and although most service providers usually design their loads to be less that 12kW (supplelemented by on-peak panel heaters), I see no problem with a 60A service fuse for 15kW. Those service fuses are far more tolerant of such slight overloads than you might think.



    Lucia.
     