Does fitting a separate CU preclude testing existing circuits

Discussion in 'Electricians' Talk' started by Lokkars Daisy, Oct 25, 2012.

  1. Lokkars Daisy

    Lokkars Daisy New Member

    In the course of my much varied enterprise I happened on this opinion
    Connecting a new circuit into an existing consumer unit requires checking of existing circuits.
    Breaking into the meter tails fitting a Henley box and a separate consumer unit reduces the responsibility for checking and signing off the existing wiring

    Is there any truth in the above, and if so, why?
     
  2. seneca

    seneca Screwfix Select

    Adding a new circuit to an existing c/u only requires testing of the new circuit and earthing and bonding etc. Lokks, no requirement to test all the existing circuits.
     
  3. Lokkars Daisy

    Lokkars Daisy New Member

    That's true seneca, so if you were to fit a separate consumer unit for a for an aditional circuit would there be any less testing involved, I'm sure not, but just running this up the flagpole . The above comments re testing , are from a manufacturers advice with reference to connecting a solar panel to an installation
     
  4. Mr. Handyandy

    Mr. Handyandy Screwfix Select

    Surely you'll be altering the characteristics of the supply(1 supply SHARED between 2 distributions), which may affect all other parts of the installation, so they should all be tested for ok?

    No ?

    Mr. HandyAndy - Really
     
  5. seneca

    seneca Screwfix Select

    I can't see there would be any less testing required Lokks, you'd still have to test the new circuit and earthing, 
     
  6. Lectrician

    Lectrician Screwfix Select

    Yep, only test your new circuit whether it be from a new small CU or the original.  If you had to replace the old CU to make room for spare ways, you would have to test all.
     
  7. seneca

    seneca Screwfix Select

    That's correct Handy, as you said NO.
     
  8. unphased

    unphased Screwfix Select

    I agree with sen. :)
     
  9. wally

    wally Screwfix Select

    I agree with sen & Lec
     
  10. Lokkars Daisy

    Lokkars Daisy New Member

    I agree with sen, lec & un

    the manufacturer has had a bum steer
     
  11. J.P.

    J.P. New Member

    Irs like when you build an extension. Whip in a DB specifically for said, and forget messing with the existing DB.
     
  12. Lokkars Daisy

    Lokkars Daisy New Member

    Yeah JP , forget about messing about with existing stuff but constaints are still the same
     