Does outside buried conduit need sealing or a drain hole?

Discussion in 'Electricians' Talk' started by Pinkspark, Feb 11, 2024.

  1. Ha ha, he wasn't worthy mate.
     
    Astramax likes this.
  2. Astramax

    Astramax Super Member

    Must be another upgrade on the way...Screwfix Super Member!
     
  3. Bob Rathbone

    Bob Rathbone Screwfix Select

    Just responding to your posting. The epoxy resin joints that you dig up and replace have not been made correctly or has been disturbed. These joints are widely used by REC's and the failure rate due to leakage is small. Failure rate due to overload is significant. SWA cable sheath when undamaged is waterproof, just as an MDPE water pipe is waterproof, it's the terminations that are water resistant, if made correctly.
     
  4. bright_Spark

    bright_Spark Screwfix Select

    you are more than likely right there bob
     
  5. bright_Spark

    bright_Spark Screwfix Select

    I cannot believe it, i am obviously being groomed for better things. Who knows what we will have to see.
     
    WH55 likes this.
  6. Pinkspark

    Pinkspark New Member

    Thanks all for your replies. To answer the specific question about why the conduit is there, the owner laid it so that it could be used to pull other through in the future if necessary (yes it's overkill, it's only 4 meters down the garden, but that's fine).
    I'm not sure about putting a drain hole in, it's just going to fill up when the ground is waterlogged, surely. Any other comments on that?
    Is the consensus to use some sealant at either end of the conduit then?
    Thanks.
    PS. You're all super members (flattery will get me everywhere)
     
  7. Coloumb

    Coloumb Screwfix Select

    If it's only 4m can't you just re-trench it and bury the (XPLE) SWA direct? I'd bed it in a bit of fine sand myself
     
  8. The Happy Builder

    The Happy Builder Screwfix Select

    Nothing wrong with SWA in buried conduit, but the SWA is not made to be permanently submerged in water, so any water in the conduit really needs to drain away.

    Armoured cables
    While Prysmian’s Low Voltage and Medium Voltage armoured cables, with both LSOH and PVC sheaths, are suitable for installation in ‘free draining soils’ they are not recommended for installation in permanently waterlogged ground, such as in clay soils or below the water-table. In free draining soils a cable can be expected to achieve Prysmian’s estimated minimum design life of 25 years for a cable fully and continuously loaded. However, in permanently waterlogged ground a cable’s design life will prematurely shortened by water migrating through the cable sheath and potentially corroding the cable’s armour.
    Electric Cables in Water? | Prysmian Group
     
    Ind spark likes this.
  9. The Happy Builder

    The Happy Builder Screwfix Select

    Fifteen years more than the design life in free draining soil.
     
    bright_Spark likes this.
  10. BuildingMad

    BuildingMad Screwfix Select

    I am wondering if longevity is a factor when the cable is below the frost line.
     