    EICR code for hob ignition wired directly into a 32 amp cooker circuit with no FCU, anyone?

    I'm thinking C2
     
  2. MGW

    MGW Screwfix Select

    Why is it coded? This is the problem, need to read manufactures installion instructions to know maximum feed size.
     
  3. Paco de Lucia

    Paco de Lucia Member

    ....on 0.75mm flex..
     
  4. jonathanc

    jonathanc Guest

    C2 and why not?
     
  5. Comlec

    Comlec Screwfix Select

    If it is a fixed load and does no exceed the cable rating then what reg are you going to use to support a C2?
     
  6. Lectrician

    Lectrician Screwfix Select

    If thermal constraints are met during a fault. A fixed load cannot overload a cable, but you need to make sure the undersized cable will survive and not be damaged by fault current.
     
  7. Paco de Lucia

    Paco de Lucia Member

    ...fault current emitted through the spark?
     
  8. The Happy Builder

    The Happy Builder Screwfix Select

    C2.

    However the FCU can be at the hob end of the reduced size cable, so long as it’s less than 3.000 metres. Which isn’t very elegant, but complies with the regs.
     
  9. spinlondon

    spinlondon Screwfix Select

    No code.
    Fixed load, not likely to overload.
     