Electric wire spec for connecting LED lights
Discussion in 'Electricians' Talk' started by AndrewLivingstone, Sep 14, 2021.
  1. AndrewLivingstone
    AndrewLivingstone New Member
  2. MGW
    MGW Screwfix Select
    Most LED no problem, but you don't say if before or after any driver, or size of LED lamps, so can't be 100% sure.
  3. AndrewLivingstone
  4. MGW
    MGW Screwfix Select
    Advert and spec sheet as much good as chocolate fire guard, it does not say what voltage, I would assume 230 volt, but it does not say 230 volt, so yes likely cable OK, but rather a daft advert, personally I would not trust a firm who do not say what voltage.
  5. FlyByNight
    FlyByNight Well-Known Member
    The installation instruction do say 220-240v but that should be on te main page. They also show an earth being needed, and with a current consumption of 0.04A (inrush up to 0.7) that 1.5mm is need. The OPs choice, is only two core so not suitable.
  6. SIRJOHN19
    SIRJOHN19 Active Member
    Second pic in the manual clearly shows, connect to mains 220-240v
  7. Bazza-spark
    Bazza-spark Screwfix Select
    It is also clearly marked in the 4th line of the installation instructions. @0.04A each 1.0mm2 will be fine, but the fittings must be earthed.
  8. FlyByNight
    But they also say 3x1.5 ... in either 6262Y or R02V giving flex or T&E but as you indirectly suggest, overkill.
  9. Bazza-spark
    Missed that one.
  10. AndrewLivingstone
    Yes, I was also not sure what input it needs so went through manual. Earth is optional. I think I'm good with that wire?
  11. Bazza-spark
    Why would you think that the earth is optional?
  12. AndrewLivingstone
    Sorry I misread it. Yes, I need three wire.