Electrician Completing Another’s Work?

Discussion in 'Electricians' Talk' started by Alex Reynolds, Nov 24, 2021.

  1. The Happy Builder

    The Happy Builder Screwfix Select

    As said by Michael Caine in The Italian job “You were only supposed to blow the bloody doors off!”
     
  2. Bazza-spark

    Bazza-spark Screwfix Select

    I thought it was slightly different to that lol :D
     
  3. The Happy Builder

    The Happy Builder Screwfix Select



    The MCBs are almost certainly rated at 6KA which is 6000 amps, as a unit backed up by the DNO fuse it will disconnect up to 16kA, but the consumer unit won’t any use afterwards.

    I would assume the PSC is more like 1.6kA, but it looks like there’s an additional digit on the scribbled note on the back board.
     
  4. Comlec

    Comlec Screwfix Select

    Looks like he ran out of Cig packets and had to write on the wall. :)
     
  5. The Happy Builder

    The Happy Builder Screwfix Select

    To be honest I would be more concerned about the piece of plywood used as a consumer unit back board than what is written on it ;)
     
  6. MGW

    MGW Screwfix Select

    I think you have missed the point? 1398.7 amp at 230 = 0.164 Ω and 0.17 Ω = 1352 amps so they seem to match each other.
     
  7. The Happy Builder

    The Happy Builder Screwfix Select

    Would you not just record the reading on your test meter?

    This discussion has well and truly lost the plot, no doubt the guy does a good job overall.
     