Garden consumer unit

Discussion in 'Electricians' Talk' started by bigfranky145, Jul 10, 2024.

  1. bigfranky145

    bigfranky145 Member

    Is it possible to have a separate smaller consumer unit for the garden coming off the main consumer unit?
     
  2. Refuse to Bend

    Refuse to Bend Active Member

    If it is suitable for the environment.
     
    bigfranky145 likes this.
  3. WH55

    WH55 Screwfix Select

    Theoretically yes, although there are limited circumstances where that would be necessary as opposed to the (sometimes easier) alternatives. Also, installing a new CU isn’t really a job for a DIYer.

    You really need to give us a bit more information on what you’re trying to achieve, and why you want a secondary CU.
     
  4. bigfranky145

    bigfranky145 Member

    Thanks - I was more asking theoretically before I ask an Electrician.

    The house has a "supply" to the exterior which was installed fairly recently connected to the CU and terminating in a box but "capped".

    I had wondered if I would need a secondary CU to have external sockets & lights hooked up to rather than take the supply from the main CU
     
  5. Coloumb

    Coloumb Screwfix Select

    What's the rating of the breaker feeding the cct?
     
  6. bigfranky145

    bigfranky145 Member

    What is the CCT? I'll have to get back to you on that (not currently at home)
     
  7. Coloumb

    Coloumb Screwfix Select

    Circuit.
     
  8. Bob Rathbone

    Bob Rathbone Screwfix Select

    Don't sound promising here. I know I keep banging on about this but circuits feeding equipment outside the zone protected by the equipotential bonding will have a shorter disconnection time than those in the zone (house). To ensure this on alny supply type, it is advisable not to export the CPC from the supply, but to use an earth electrode locally to the new CCU and fit a 30mA rcd to protect all circuits. If the CCU is in a damp area it should be non flammable non metallic as would be used in agriculture and horticulture.
     
  9. Refuse to Bend

    Refuse to Bend Active Member

    Might help if you could direct me as to the applicable Regulations in BS7671.
     
  10. CBE

    CBE Active Member

    would you not negate that by picking the correct (larger) size cpc? More so for supplies directly outside the house lights/socket.

    agree on going down the bottom of the garden depending on size etc. each job is different and takes that in to account.

    i have heard of what you mentioned about exporting it and i think it was more to do with the dno and are different regs, also something about the incoming cable gland to the sub ccu needs to be plastic not metal so that it doesn’t do what you mentioned. That was word of mouth though and haven’t looked in to it personally (as I haven’t needed to).

    if anyone has any further info would be good to know.
     
  11. WH55

    WH55 Screwfix Select

    Depends on circumstances but might be easier to run a direct supply, eg SWA, to a socket radial circuit (no CU) then fuse down for lights. A new CU is probably unnecessary unless you’re going for high powered tools / equipment and various sheds etc.
     
  12. The Happy Builder

    The Happy Builder Screwfix Select

    As the DNOs will tell you, use of TNCS earthing is not recommended in BS7671 Section 705 due to the reasons that Bob gave. See 16.4 in the SP Energy guidance
    https://www.spenergynetworks.co.uk/userfiles/file/EART-01-002.pdf

    Some DNOs may just refuse to connect a new supply depending on the circumstances.

    Unless carefully planned and specified, use of a DNO TNCS earth is not a good idea for a garden installation.
     
  13. malbec4

    malbec4 Screwfix Select

    Section 705 refers to agricultural installations. There's a lot of talk regarding livestock and the use of 100ma and 300ma RCDs. There's also a reference to electric fences. SP Energy 16.4 also refers to Section 705. I don't think it is intended to address somebodies garden.
     
    Coloumb and Refuse to Bend like this.
  14. Refuse to Bend

    Refuse to Bend Active Member

    Not really sure how that is applicable. #8 refers to shorter disconnection times, outside zones etc.....
    I am interested where this is referenced.
     
    Coloumb likes this.
  15. adgjl

    adgjl Screwfix Select

    It is a bit of a mess unfortunately. It used to be in the PME Regulations, which were a supplement to the old Supply Regulations, and were both Statutory Documents. Unfortunately, when the UK government of the day wrote and implemented the ESQCR regulations, the PME regulations were forgotten about and not included. They do still exist very much in the "DNO World" for ensuring connections to the public supply are safe, and have had to be incorporated into the various DNOs Technical Guides, which in general are for DNO staff only, albeit a few DNOs have made their various Technical Guides available on the internet.
     
  16. Refuse to Bend

    Refuse to Bend Active Member

    And how do the DNO "police" the installation after their meter and how is it their business?
     
    Coloumb likes this.
  17. adgjl

    adgjl Screwfix Select

    The ESQCR makes it their business. My employer (a DNO) insists on a Test Certificate from a person or company registered as "Competent" for Building Regulations "Part P" signoff for a new property, re-wire of an existing property, or certain other specified works such as solar, battery or wind generation. No certificate, no supply. Simple.
     
  18. Coloumb

    Coloumb Screwfix Select

  19. The Happy Builder

    The Happy Builder Screwfix Select

    If the installation is TT earthed, disconnection times are shorter, unless you fulfil requirements that cannot be fulfilled outdoors in a garden, because you are outside any equipotential zone you may have created within the indoor installation.
     
  20. WH55

    WH55 Screwfix Select

    Indeed. The DNO I worked for was the same. Different DNO as I’m in Scotland.
     