Get your Ra's down!

Discussion in 'Electricians' Talk' started by sparky Si-Fi, Feb 29, 2004.

  1. sparky Si-Fi

    sparky Si-Fi Screwfix Select

    Just an enquiry,does anyone here know of the name of the product that resembles a cement or concrete with some mettalic compound in it that helps you out if you got a really high RA reading off an earth spike?.
     
  2. supersparky

    supersparky New Member

    yes mate, its called running out of sand and using alli fileings...
    (might be one to try actuly....)

    ss
     
  3. sparky Si-Fi

    sparky Si-Fi Screwfix Select

    Evenin m8 how we doing?...thing is I am in the middle of a job and after banging a rod in I got an Ra of 300 ohms! everything checked out,heres me thinking,I cant keep banging loads of rods in this guys garden or else its gonna end up looking like the Avebury stone circles!!

    Saying that though,with that reading and a bit of Maths gives me...Ra*I^n < 50 V so 300*.100=30 so to me it complies.

    Would be nice to get it down it bit more!
     
  4. supersparky

    supersparky New Member

    maybe that is an idea....just dig a cubic meter over and add a few kgs of alli powder....

    ss
     
  5. sparky Si-Fi

    sparky Si-Fi Screwfix Select

    Thanks for the input m8,Ill let you know what happens
     
  6. supersparky

    supersparky New Member

    LOL, you sound enthusiastic...
    (i would be :|)

    ss
     
  7. G Bush

    G Bush Member

    Hey, 300 ohm that is quite a high value. Whatever happened to metal milk crates
    There ya go
    Dubya
     
  8. Bewlec

    Bewlec Member

    Be carefull with your readings as the guidence note 3 inspection and testing states that any thing over 200 ohms should be classed as unstable try putting in parralel earth rods but not to close to each other
     
  9. socketman

    socketman New Member

    Hey dude

    Check your test equipment on known good earth...ie. at home
     
  10. supersparky

    supersparky New Member

    you could always have a wizz on it to get ur readings down!

    ss
     
  11. sparky Si-Fi

    sparky Si-Fi Screwfix Select

    Sorted it!

    The connection on top of the earth clamp was the prob...:( Gave it a real hefty tighten-up and we now got a satisfactory 37 ohms,bit weird I know!

    Just had my Robin callibrated and tested my own Ze (.08)

    Many thanks all for the input though all,

    SF
     
  12. ban-all-sheds

    ban-all-sheds New Member

    ...try putting in parralel earth rods but not to close to each other

    But not too far apart either, lest a nearby lightning strike sets up a significant PD between the two?
     