Hive receiver wiring help

Discussion in 'Electricians' Talk' started by Jamiemckenzie, Mar 11, 2018.

  1. Jamiemckenzie

    Jamiemckenzie New Member

    Hi,

    I'm just trying to wire my Hive receiver. It's just a simple set up at the min. Boiler to wired thermostat. See pictures you can tell what one the old thermostat is.
    I do only have 3 wires plus a earth which I believe you don't really need. L N and I presume 3 is a switch for the boiler.

    I've followed the wiring diagram but when I press the central heating button on reciever the boiler does not fire up as it says it should in the instructions.
    I've took a link from L to COM as I thought I would need this. Ive attached pictures of my old thermostat and new receiver. I have not install receiver against the wall on the pic as I am moving it closer to the boiler and want to ensure it works first.
    I've also I attached a pic of the existing wiring diagram for my thermostat and wiring for new receiver. It's abit unusual but they have the L cable as black rather than Brown which is abit strange.

    Any help would be much appreciated.

    Thanks
     

    Attached Files:

  2. Mike83

    Mike83 Well-Known Member

    What make and model of boiler do you have.
    Do you have a programmer?
     
  3. Jamiemckenzie

    Jamiemckenzie New Member


    Robbie, I've wired the black into the L port of the receiver?

    Regards
     
  4. dobbie

    dobbie Well-Known Member

    Sorry my mistake,I would check anyway as it would not make any difference on the old stat.
    I Need to go to specsavers.
     
  5. Mike83

    Mike83 Well-Known Member

    The black needs to be a permanent live.
    Usually it only becomes live once a programmer is switched on.
     
  6. Bazza

    Bazza Well-Known Member

    ........as Mike says. And he did ask you before for good reasons.....
    If you have a programmer, and it is still in circuit, you will have to set it to constantly on, or the timings on that will over-ride the Hive.
     
  7. Jamiemckenzie

    Jamiemckenzie New Member

    Hi,
    Boiler is a worcester 29 cc1 boiler,
    This does have a timer. Would you suggest to have the timings to constantly on?
     
  8. Bazza

    Bazza Well-Known Member

    Do you not read the advice you are being given.?
    My post #6 above says just that.
     
  9. Mike83

    Mike83 Well-Known Member

    Leaving the timer constantly on will give the hive it's permanent
    live that it requires.
    Turning the timer off will kill the live to the hive.
     
  10. Jamiemckenzie

    Jamiemckenzie New Member

    Spot on thanks will try that tomorrow.
     
  11. Jamiemckenzie

    Jamiemckenzie New Member

    20180313_170949_resized.jpg Hi, have not had to have another go of wiring receiver yet but I've took a pic of the boiler wiring.
    Brown from spur socket goes to L, then blue from spur socket to neutral.

    Then going to thermostat at the min is blue from N, black from Ls then brown from Lr.
    Looking at the pictures from earlier and from this, would you still suggest it wasnt working due to the timer not being permantly on or switch any wires around?

    Thanks
     
  12. Mike83

    Mike83 Well-Known Member

    Wires are correct.
    The black into Ls supplies the room stat with power only when the programmer is at 'on' or on a timed period.
    So when the programmer is off the stat won't have any power.

    Leave the programmer at on permanently. Then wire up your stat just as you thought.
     