Hob supply

Discussion in 'Electricians' Talk' started by seneca2, Sep 2, 2010.

  1. seneca2

    seneca2 New Member

    Hi all,
    I need to install a dedicated circuit for an induction hob, max load is 9Kw, it's not a very long run but i'm wondering whether to run it in 10.0mm rather than 6.0mm, is this being a bit ott?
     
  2. gerrin2owd

    gerrin2owd New Member

    6mm on a 40A mcb will be fine Sen, after all your old fashioned slot in cooker has a max load of around 12k. Diversity and all that stuff you know :)
     
  3. seneca2

    seneca2 New Member

    Yes you're right gerrin, it was just a thought!
     