Honeywell 3-Port Mid position Valve
Discussion in 'Plumbers' Talk' started by Studentrooms, Nov 14, 2017.
  1. Studentrooms
    Studentrooms Member
    I need to change a Honeywell , 3 port, Mid positon heating valve,
    not sure if it's a 5 wire or if they also do 4 or 3 wire types....
    simply want to get both and fit the one required when I get there....
    but can't find reference to anything other than 5 wire types...
    so starting to think they are all 5 wires.....
    sound right ?
    Thanks
  2. I think, almost certainly, a Honeywell 3-port valve will be a 5-wire jobbie.
    Can you ask the owners to look at the model number on the valve case - is it V4073A?
    Are you a 'pro' or a DIYer? If the latter, a good tip is - once you've fully isolated the power - to snip the 5 old wires a couple of inches from the wiring centre so's you can still ID them, and then replace them one at a time - grey for grey, white for white etc...
    Dr Bodgit likes this.
  3. Dr Bodgit
    Dr Bodgit Well-Known Member
    My valve is a Honeywell 3-port V4073A jobbie...with 5 wires. Took me ages to spot one of the wires though as it was obscured in the enclosure.
  4. The V4073A is def 5 wire (one's an earth).
  5. Dr Bodgit
    Valve wiring configuration is:
    White = Heating on
    Blue = Neutral
    Grey = Hot water off
    Green/Yellow = Earth
    Orange = Boiler and pump live
    So you need 5 wires in order to independently switch CH and HW, together with a live (to boiler), neutral and earth. A 4 wire 3-port valve would make no sense.
  6. leesparkykent
    leesparkykent Well-Known Member
    The three wire (brown,blue green/yellow) 3port diverter valve part number is V4044. Commonly used on priority hot water systems in places with high hot water demand. Sometimes referred to as a W-plan.
    Deleted member 33931 likes this.