Ideal Logic Combi Flame Loss problem - advice needed
Discussion in 'Plumbers' Talk' started by Andy Grow, Dec 8, 2018.
  1. Andy Grow
    Andy Grow New Member
    Hi!
    I bought a house with a boiler installed Ideal Logic 30 Combi. I don't have warranty on it, although it's rather new, of 2015. The whole system has been drained flashed and resealed.
    When I moved in I was just using hot water. When I switched on CH mode, boilers makes a noise before stopping and shows F2 on screen (flame loss). The blue light appears for a few seconds only.
    So, if the blue light switches on for 3-5 seconds and goes down, does it actually count as ignition has started to burn?
    Can it be something to do with a flame detector, or ignition electrode, or spark generator?
    Also I've noticed a small hole in a silicone cover over flame detector electrode, can this be a reason? (on a pic)
    My engineer is abroad now and I'd like to find the reason just to get an understanding how serious the fault is. Is it easy to fix or the whole boiler needs to be changed?
    Thanks in advance!
  2. ajohn
    ajohn Member
    This might help page 52
    https://acwilgar.co.uk/Boiler-Manual-PDF/Ideal/Logic-Combi-Installation-Manual.pdf
    Very probably nothing to do with your problem but we had an older style simpler boiler cut out on central heating at times. Called Worcester and they sent an engineer. No fault. Still did it so they came again. Claimed that the gas valve was faulty as it suddenly shot up and replaced it. I asked if they were sure it wasn't just a worn pump - no. Guess what it was. The boiler runs at more kw when heating water hence the reason it shot up. Just mentioned because of the last fix in the fault finding chart. I believe that when the do act up it's usually a jam of some sort. I'm no plumber or installer though.
    John
  3. Andy Grow
    Thank you John!
  4. Mike83
    Mike83 Well-Known Member
    Does the boiler have the same fault on heating and hot water or heating only.
    Usually if the boiler has an ignition fault it will affect the operation of both heat/hw
  5. Andy Grow
    Well at the beginning it was just on heating, hot water was ok. Now it is on both.
  6. Mike83
    Are the other gas appliances in the house still working?
    Otherwise it sounds like an ignition issue.
    First thing I would check is the condensate trap.
  7. Andy Grow
  8. The Teach
    The Teach Well-Known Member
    the idea of asking that question is to establish if your property is getting sufficient gas pressure for your boiler to ignite,if you have a gas hob or other gas appliance turn it on full and check the flames are reaching the usual height.
    Maybe consider getting Ideal to repair then service your boiler,seen many ignition faults on logics. Ranging from lack of (correct) servicing to component failure. The flame detector is not usually a fail item ;).
    Them boilers need some tlc from competent service technicians,they have a few unusual faults :(
  9. Andy Grow
    Thanks for your reply.
    Well, we don't have anything else running on gas in the property.
    This is the problem: as this boiler had been installed before I moved in, I don't have warranty and it will be quite costly to get the Ideal engineer to check it, especially if it turns out the whole boiler will have to be changed.