Hi, I’m new to the forum. I’m looking for some help!! I need to install a relay to switch a lighting circuit. This relay is to be switched via an AV system. When the tv screens come on, the lights go off. The AV guy has asked for a 0v no contact to connect his system too. I was told by Hager that an ERC218 relay will do the job. I just don’t know how to wire it. it basically looks like a contactor that I’m familiar with. Can anyone help, or suggest something else I can use? Thanks
The relay has a 230 Vac coil and a set of N/O contacts and a set of normally closed which are volt free. However I can't make out what you want to do? Switch on the TV at same time as switching lights off, or switching lights off as you switch TV on? If former then use a double pole light switch, if latter then not sure if a 230 Vac relay would do the job? There is also the point the relay needs to be fitted in an enclosure, and this is where we start to look at other options, for example if the 13A socket was a wifi controlled one and the light switch was also a wifi controlled one, you could program the same button to do both, so single press of a remote control button with do both functions. Likely better would be different buttons on same remote.
Ok so basically. Soon as the AV System turns on (cinema room) lights go off. The av has a 0v NO contact as it’s switch for this. Once the AV system has finished doing its thing or switches off the lights come back on. I assume the Av will just open and close a contact. As long as I provide a 0v NO contact for the av guy that’s down to him to sort. I’m just doing the lighting side, (230v side of things) Cheers
So with you saying the contacts are volt free, if I was for example to use a link (piece of wire) and held it on the contacts, that would pull the relay in?
This sounds beyond you. Your av is providing a volt free contact. Use that to switch a suitable rated contactor controlling your lights.