Maximum permitted Zs Values recorded on Certificates

Discussion in 'Electricians' Talk' started by unphased, Nov 8, 2007.

  1. Lokkars Daisy

    Lokkars Daisy New Member

    Also, on a normal TN split load board . The 30mA rcd is also providing protection against indirect contact (along with supplementary protection against direct)
    Who would argue that it is not admissible to fill in all your Zs boxes with 50/30mA =1666 Ohms after all despite the type/size of mcb s fitted 1666 Ohms is the max Zs permitted value ?
     
  2. Lokkars Daisy

    Lokkars Daisy New Member

    No objections then,we are all agreed, how about you Lucia and Captain Sir ?
     
  3. sparky Si-Fi

    sparky Si-Fi Screwfix Select

    Well thankfully my Palm lists all the Max values when I compile my certs,so its always gone in

    You do 'em enuff and you memorise the most commom especialy the common as muck type B's

    6A 8.00
    16 3.00
    20 2.40
    32 1.50
    40 1.20
     
  4. ban-all-sheds

    ban-all-sheds New Member

  5. ban-all-sheds

    ban-all-sheds New Member