No hot water - do I need 28MM gas pipe?
Discussion in 'Plumbers' Talk' started by Harriet Davies, Jan 12, 2018.
  1. Harriet Davies
    Harriet Davies New Member
    Thanks for your advice, I have contacted the original installer and coming to inspect next week
  2. andy48
    andy48 Active Member
    If the pressure is 24 milli bars (mb) at the meter and 13 at the boiler, then the pressure drop is 11 mb. The pressure drop is not allowed to be more than 1 mb at any working appliance. However:
    a. 24 mb is high for pressure at the meter. The regulator is meant to keep it in the range 19 to 21 mb although it has been known to be a bit higher.
    b. What needs to be measured is working pressure at the meter and working pressure at the boiler with the boiler running full blast. The difference between pressure at the boiler and pressure at the meter should not be more than 1 mb. If it is more, then the pipe is under-sized or there is an obstruction.
    c. Working pressure at the boiler should be between 15 and 23 mb measured at the test point. Can't remember, but I think Vaillant's pressure at test point is usually a few mb less than if the pressure were actually measured at the gas pipe as it enters the boiler.
    d. It is possible for the gas meter regulator to be faulty. Be suspicious if the standing pressure reading fluctuates. It can be caused by water in the mains, but can also indicate a faulty regulator.
  3. Harriet Davies
    Performance readings were fine when installed
  4. Harriet Davies
    The meter has been changed, 18 months ago - could this be the reason?
  5. Harriet Davies
    Should i call British GAs to check the meter regulator?
  6. retiredsparks
    The Gas Engineers on here should be able to offer better advice...when they come along.
    Rs
  7. longboat
    longboat Well-Known Member
    Do you have the paperwork for the boiler, and has the the benchmark check at the back been filled in?
    What are the recorded values for gas pressure at the meter and boiler when it was commissioned?
    I take it this fault hasn't been happening since it was installed ?
  8. Isitreally
    Isitreally Well-Known Member