Prelim of PIR for a retail unit

Discussion in 'Electricians' Talk' started by Real Spark, Jan 21, 2007.

  1. Real Spark

    Real Spark New Member

    Date of installation April 2006

    Electrical Installation

    Description of deviations (where Applicable)
    BS 7671

    A periodic inspection notice is not displayed

    Warning notice non standard colours not displayed

    32amp MCB fitted to lighting circuit wired in 1.5 T&E cable

    Low energy down lights CPC (earth wire) connections, twisted together, not
    terminated & no sleeving (29No)

    Low energy down lights fitted through ceiling tile with no other means of support

    CPC connection to 600x 600 lighting modules twisted together
    with only one CPC connected to earth terminal (39 No)

    Cables not fixed laid on ceiling grid

    Wiring not identified no coloured sleeving

    Water pipe no earth bond

    NIC EIC cert issued first 3 pages only, no test results, even worse the installer is not an NIC member


    RS
     
  2. sinewave

    sinewave Screwfix Select

    Sounds a very standard setup!


    Especially the cables laid on the ceiling grid! ;)
     