RCD not tripped but sockets out in one room.

Discussion in 'Electricians' Talk' started by Rainyday, Aug 1, 2021.

  1. Rainyday

    Rainyday New Member

    We are having building work done to our house and having bathrooms redone at the same fine by a different company. We have just come back from a week away to our utility room having no power. The RCD hasn’t tripped for the sockets but the lights were tripped when we came in. There has been a leak in the bathroom above the utility and water has come through the ceiling. The electrician for the bathroom f
     
  2. Rainyday

    Rainyday New Member

  3. Rainyday

    Rainyday New Member

    The grey cable going into the box is the new wiring for the shower. Could this have caused an issue?
     

    Attached Files:

  4. Rainyday

    Rainyday New Member

    We are having building work done to our house and having bathrooms redone at the same fine by a different company. We have just come back from a week away to our utility room having no power. The RCD hasn’t tripped for the sockets but the lights were tripped when we came in. There has been a leak in the bathroom above the utility and water has come through the ceiling. The electrician for the bathroom has installed a new cable for the shower and installed this into the RCD box. We have reset the RCD but still no power.
     
  5. Bob Rathbone

    Bob Rathbone Screwfix Select

    I would guess that the bathroom fitters or the builders have damaged a cable or disconnected something. You need an electrician to find out what is wrong and if it is caused by the work being done, you can charge the company responsible.
     
  6. spirits are real 2016

    spirits are real 2016 Screwfix Select

    Can you post more photos further away showing all the boxes next to consumer unit that switch is not rcd but the main switch to turn the house off.
    Also even tho they haven't tripped turn off all the MCB,s and turn them back on one by one the power might come back on..
     
  7. Shaun Mitchell

    Shaun Mitchell New Member

    Maybe when
    Maybe a cable has been dislodged in your consumer unit whem the shower cable was put in or could be a faulty mcb power not going through to the load side sometimes Turing it off and on a few times can reinstate it
     