Summer House TT

Discussion in 'Electricians' Talk' started by Philip Hyde, Apr 15, 2019.

  1. Philip Hyde

    Philip Hyde Member

    Not done very much on TT stuff. But got roped in to wiring my brothers summer house. The main house is on a TT. So plan is supply via 10mm SWA to house and connect to a MCB in the exsisting board. My question is about the earth. Was going to earth both ends of the armoured and also fit a new electrode and the summer house end. Whats your thoughts?
     
  2. peter palmer

    peter palmer Well-Known Member

    Thats how I would do it, although some say you only need to use the main house earth rod. I think 2 rods is better than one.
     
    Philip Hyde likes this.
  3. Philip Hyde

    Philip Hyde Member

    Thanks Peter.
     
  4. Lucky13

    Lucky13 New Member

    no real point putting in additional rods the house one will be enough. You said connect to an existing MCB I assume that MCB is backed up by and RCD of some sort?
     
  5. peter palmer

    peter palmer Well-Known Member

    Best to supply it from its own unit with a time delayed RCD in really so you don't have to run back to the house if something trips.
     
    Philip Hyde likes this.
  6. Philip Hyde

    Philip Hyde Member

    All done and added the additional rod. Dropped EFL in house from 46 ohms to 25 ohms!
     