Towel rail
Discussion in 'Electricians' Talk' started by MJA, Mar 12, 2010.
  1. MJA
    MJA New Member
    Electric towel rail in bathroom fed from lighting circuit (6A 60898 type B with 30mA 61008 RCD) via double pole pull cord with neon outside zones.
    Does this compy with BS7671 ?
    Cheers
  2. sysparks
    sysparks New Member
    what is wattage of towel rail?
  3. seneca2
    seneca2 New Member
    Sound's ok.
  4. MJA
    MJA New Member
    150w
    Ta.
  5. sysparks
    sysparks New Member
    As said, sounds fine.
  6. MJA
    MJA New Member
    ok cheers.
    Couldn't decide whether 3amp FCU might be required as is the case with an extractor fan.
    Thanks for replies
  7. Chuck Wanoff
    Chuck Wanoff New Member
    Not required
  8. seneca2
    seneca2 New Member
    If it's on a 6amp breaker no fcu required, (same with a fan)
  9. pearcy
    pearcy New Member
    Not required
    since when was you the manurfactuer
  10. Chuck Wanoff
    I'm not a manufacturer, but the fact remains that the fcu is not required.
    Manufacturers only issue guidelines anyway, and it would be foolhardy to follow their instructions blindly.
  11. seneca2
    seneca2 New Member
    Fan manufacturers literature often says to use an fcu with 3amp fuse if not being fed from a 6amp circuit (or words to that effect).
  12. MJA
    MJA New Member
    blindly.
    Actually my assessor this year highlighted that manufacturers instructions MUST be followed even if they go beyond the requirements of BS7671. This is specified in the 17th edition.
    Most fan instructions state a 3A fuse required unless the circuit is protected by a 5A fuse or less. Personally I never install a FCU on a fan but always an isolator switch, despite manufacturers instructions.