Tricky fault......ideas please
Discussion in 'Electricians' Talk' started by Jimtnash, Mar 13, 2018.
  1. Jimtnash
    Jimtnash New Member
    Hi,
    Have an 18 month old Consumer unit, suddenly started tripping out RCD, lighting circuit mcb is the culprit.
    Have: replaced rcd , replaced mcb, removed lamps. Not a borrowed neutral....... ideas please.
    Many thanks.
    Jim
  2. JP.
    JP. Screwfix Select
    Is the cu a Crabtree Starbreaker Jim?
  3. Jimtnash
    Jimtnash New Member
    J.P.
    Thanks for prompt response.....no it is a schneider Easy 9
    Jim
  4. Dr Bodgit
    Dr Bodgit Well-Known Member
    Could be a loose or bare wire, neutral touching backbox or earth for example.
  5. JP.
    JP. Screwfix Select
    Is it the upstairs or downstairs lighting circuit which is tripping the rcd Jim?
  6. 14th edition
    14th edition Well-Known Member
    So if you disconnect the L/N for the lighting circuit and test for IR what readings do you get?
  7. JP.
    JP. Screwfix Select
    Sounds like the downstairs lighting circuit to me. Are there any external lanterns on this circuit Jim? ie..security light/s/bulk head type units/lamp post/s etc etc?
  8. Jimtnash
    Jimtnash New Member
    Yes - there are external lights on this one (it is downstairs lights) - will try and track them down -thanks jim.
    (Have looked for loose wires /shorts but all good dr bodgit -thanks though)
  9. Bazza
    Bazza Well-Known Member
    RCDs are made to trip when there is an earth leakage. There are stories about RCDs that have tripped because of an L-N short circuit, or a loose wire but generally they don't care about such things.
    Unless you spot something obvious in the soggy outside light department, then you'll be much more likely to find a problem using proper test equipment.
    Guessing and hoping is a long, frustrating road to nowhere.
  10. Jimtnash
    Jimtnash New Member
    Guessing & hoping worked !! Found stray, loose live after couple of hours. Thanks for input one and all !
    Jim
    Bazza likes this.
  11. Bazza
    Congrats. I guess it works sometimes!
  12. Dr Bodgit
    Sometimes you actually find the needle in the haystack!
  13. JP.
    JP. Screwfix Select
    Where was that stray loose live Jim?
  14. Lectrician
    Lectrician Screwfix Select
    Where does this assumption come from?
  15. Lectrician
    If turning off the lighting MCB cures the tripping issue, it won't be a N to E fault.