    Hi have a CU change existing Ze 180ohms not acceptable for CU change. Cant find rod could be under concrete floor so cant guarantee condition etc
    So adding another rod & 6mm to MET, so do i class Ze of new rod etc as Ze or am i allowed to use both? baring in mind i can guarantee condition of the first rod & cable as it disapears in conduit in concrete floor?

    Ant
     
  2. 2 wheeled ant

    2 wheeled ant New Member

    Thanks girls & boys take it thats a
    havent got a clue answer


    Ant
     
  3. M107

    M107 New Member

    I'd go for a new rod (10mm conductor personally) & record that as the Ze as you say you cant verify the old one.
     
  4. M107

    M107 New Member

    Was in the middle of replying seen as no one else wanted to venture a reply matey :)
     
  5. general matter's

    general matter's New Member

    me personally ant would install new rod and get rid of old rod! it cannot be traced, inspected, tested etc so has to go!
     
  6. M107

    M107 New Member

    Bit like buses none at all then 3 turn up together.
     
  7. general matter's

    general matter's New Member

    or you could if ya want install new rod, record Ze on that rod! then parallel it for supplementary purposes ;)
     
  8. 2 wheeled ant

    2 wheeled ant New Member

    or you could if ya want install new rod, record Ze on
    that rod! then parallel it for supplementary purposes
    ;)

    Thats what i was thinking as seems a waste to cut cable.
    But thanks a problem shared is a problem halved!

    Ant
     
  9. general matter's

    general matter's New Member

    i would buddy! ;)
     
  10. JP.

    JP. Screwfix Select

    Just stick new Rod and Pit in lud and eeee by gummm everything is ok..ermmmm hopefully..
     
  11. bs7671

    bs7671 New Member

    I was tought at college that the cable to the rod had to be 16mm. I wouldnt run 6mm if i were you.
     
  12. X

    X New Member

    I was tought at college

    Pay attention at the back....

    Have a peep at table 10c p163 OSG for starters
     
  13. X

    X New Member

    What you may of misheard was relating to the actual csa of the rod.. Brown book, Table 54A p113
     
  14. jimmythemap

    jimmythemap New Member

    link the rods to each other then still only one Ze at MET
     