We had a heat pump installed about 10 years ago and with it a Joule twin tank setup. The bottom one is the buffer tank and the top one is an unvented hot water cylinder. However, the hot water cylinder was set up vented. This was working OK until a pump was fitted. Now, particularly after the immersion has been run on a legionella cycle, the hot water pump feeding the hot taps in the house is sucking in lots of air.

I think this may be because the vent pipe is not allowing air out of the cylinder due to it not being top entry and with the added problem of going down before going along and back up again to the loft.

Is there a way to fix the problem?

Thanks,
Edward
 

Attachments

  • Picture1.png
    Picture1.png
    159.5 KB · Views: 19
  • IMG_3365.JPG
    IMG_3365.JPG
    1.7 MB · Views: 18
  • IMG_3366.JPG
    IMG_3366.JPG
    1.6 MB · Views: 15
  • IMG_3367.JPG
    IMG_3367.JPG
    1.6 MB · Views: 16
  • IMG_3368.JPG
    IMG_3368.JPG
    1.7 MB · Views: 15
Good idea, thanks. First image is the overall setup. Second one shows the outlet for the pump feeding the hot taps in the house. The third and fourth show the shower pump and vent outlets.
 
If you use a whole tank of hot water every day, the legionnaires cycle is probably unnecessary.
 
hi
the hot distribution pipe from the cylinder must go either level or up hill !
this will allow air to vent, other wise lots or air will be trapped

ideally turn the elbow from pointing down to pointing up. and then a tee off to hot supply and the vertical pipe to vent over the f&e tank